Can a Smart-UPS 3000 rackmount run on a 20A circuit?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can a Smart-UPS 3000 rackmount run on a 20A circuit?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

0 Likes
3
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

Can a Smart-UPS 3000 rackmount run on a 20A circuit?

Hi all,

We just purchased a new APC Smart-UPS 3000 rackmount UPS (specs here: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA3000RMJ2UB&total_watts=50)

The problem is that we didn't realize until after we purchased it that we are only running a 20A circuit to the wall outlet and the plug on the UPS is for 30A

I'm hoping that it was given a 30A plug to handle high-power datacenter lines and with an adapter I can run it on a 20A line. Does anyone know if it's safe to run this UPS on a 20A line?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

Angela,

I have a similar problem.  The link does not work.

[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]

Would you be able to resend the link? Thanks.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

hello,

[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]

that should answer your questions, but the answer is essentially yes, you can change the plug type but you need to worry about overload conditions.

but please take a look at the article and let us know if you have any other questions.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

I Picked a Winner comes up with good links. How did you ever find that one on APC website?

As an electrician I would say get a quote to pull #10 wire. The cost shouldn't be too crazy and there may be a 30 amp single pole breaker already in the panel.

We always run #10 even if we were to put a L520R
L(locking) 5(120v) 20(20amp) or 30(30amp) R(receptacle). Gives you more options down the road.

Good link.
http://www.maxpowercorp.com/nema.pdf

Also in the future consided operating servers at 208v or 240v to cut down on heat load and operate more efficently.

My 2cents.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:56 AM . Last Modified: ‎2024-03-08 03:50 AM

Angela,

I have a similar problem.  The link does not work.

[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]

Would you be able to resend the link? Thanks.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of