We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Hi all,
We just purchased a new APC Smart-UPS 3000 rackmount UPS (specs here: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA3000RMJ2UB&total_watts=50)
The problem is that we didn't realize until after we purchased it that we are only running a 20A circuit to the wall outlet and the plug on the UPS is for 30A
I'm hoping that it was given a 30A plug to handle high-power datacenter lines and with an adapter I can run it on a 20A line. Does anyone know if it's safe to run this UPS on a 20A line?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Angela,
I have a similar problem. The link does not work.
[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]
Would you be able to resend the link? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
hello,
[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]
that should answer your questions, but the answer is essentially yes, you can change the plug type but you need to worry about overload conditions.
but please take a look at the article and let us know if you have any other questions.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
I Picked a Winner comes up with good links. How did you ever find that one on APC website?
As an electrician I would say get a quote to pull #10 wire. The cost shouldn't be too crazy and there may be a 30 amp single pole breaker already in the panel.
We always run #10 even if we were to put a L520R
L(locking) 5(120v) 20(20amp) or 30(30amp) R(receptacle). Gives you more options down the road.
Good link.
http://www.maxpowercorp.com/nema.pdf
Also in the future consided operating servers at 208v or 240v to cut down on heat load and operate more efficently.
My 2cents.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Angela,
I have a similar problem. The link does not work.
[Take a look at this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184]
Would you be able to resend the link? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of