Bypass not in range; either frequency or voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Bypass not in range; either frequency or voltage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

0 Likes
1
12418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

Bypass not in range; either frequency or voltage

We installed a new SRT6KXLT last year and have received a few of these errors... maybe one a month.  The unit has a step-down transformer.  I have read several posts regarding the Input voltage and Output voltage.  Our Input is 220.  The Output selected on the UPS is 240.  There is only an option for 208 and 240.  Is leaving the Input at 220 going to cause any issues or do I need to have the Input changed to 240?  I would rather not have to do this.  Looking for advice and reasons why I would need to.

Current Status - Input - 221.1; Output - 239.6.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

0 Likes
0
12414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

Bypass is used when the UPS has a fault and can't run off the battery.  Normally if there is a fault (say the batteries are old and don't hold a charge) the UPS will switch to bypass mode where it simply feeds the input mains AC to the output.

However the UPS still monitors the AC input and if it goes out of range (e.g. the voltage is too high or low) then it won't switch into bypass because it doesn't want to pass that bad voltage through to your connected devices.  So the warning basically means the power quality is not good enough, and should the UPS fail and have to go into bypass, it won't - and instead it will just shut off and everything will lose power.

It's nothing to worry about as normally the UPS won't be going to bypass mode.

Having your output voltage set as high as possible provides some benefits (lower current, increased efficiency) so there is no problem having it set higher than the input.

Perhaps check what voltages you have configured as your high and low cutoffs, and adjust these if necessary.  For example if you have told the UPS that the minimum voltage you will accept is 215 V but your power occasionally drops to 210 V, then telling it you will accept passing down to 208 V through to your load will stop the bypass warnings.  Looking at the logs when these messages arrive should tell you what the voltages were at that time so you can make the decision whether that voltage is acceptable or not.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

0 Likes
0
12415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:17 AM . Last Modified: ‎2024-03-07 11:17 PM

Bypass is used when the UPS has a fault and can't run off the battery.  Normally if there is a fault (say the batteries are old and don't hold a charge) the UPS will switch to bypass mode where it simply feeds the input mains AC to the output.

However the UPS still monitors the AC input and if it goes out of range (e.g. the voltage is too high or low) then it won't switch into bypass because it doesn't want to pass that bad voltage through to your connected devices.  So the warning basically means the power quality is not good enough, and should the UPS fail and have to go into bypass, it won't - and instead it will just shut off and everything will lose power.

It's nothing to worry about as normally the UPS won't be going to bypass mode.

Having your output voltage set as high as possible provides some benefits (lower current, increased efficiency) so there is no problem having it set higher than the input.

Perhaps check what voltages you have configured as your high and low cutoffs, and adjust these if necessary.  For example if you have told the UPS that the minimum voltage you will accept is 215 V but your power occasionally drops to 210 V, then telling it you will accept passing down to 208 V through to your load will stop the bypass warnings.  Looking at the logs when these messages arrive should tell you what the voltages were at that time so you can make the decision whether that voltage is acceptable or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of