Does anyone have clear instructions for bringing a symmetra 80kva in, and out of bypass? I cant seem to find anything on APC site.
Thanks in Advance,
-Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Hi,
The procedure is documented in the PX operation guide. Page 16 on the PDF (10 on the actual document)
http://www.apcmedia.com/salestools/MHAN-7ESBDV_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Very Helpful! Thanks for finding this, its exactly what I have been looking for!
-Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Matt,
Is this just the 80k symmetra or do you also have a PDU (with Q1, Q2, and Q3 breakers)?
You can put the UPS into bypass via the Control screen on the LCD menu on the front of the UPS. If you have a PDU, you can operate the Q breakers to wrap the power around the UPS (in case of maintenance). The "safe to operate" lights come on and off below the Q breakers to let you know you can flip those switches without dropping the load.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Place the UPS into bypass via the powerview display.
Wait for the bypass light to go on, then flip Q3.
To take it out:
Flip Q3 back down, wait for th Q3 light to go out, then take the UPS out of bypass via the Powerview.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Yes it has a PDU with Q1, Q2, and Q3. I was hoping to find a step by step guide from APC, showing what to enter on the LCD on the unit, and what switch to flip & when. I have written a guide for our maintenance personel in case I am not around, but Im not sure my procedure is 100% correct.
Thanks,
-Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:56 AM . Last Modified: 2024-03-08 03:50 AM
Hi,
The procedure is documented in the PX operation guide. Page 16 on the PDF (10 on the actual document)
http://www.apcmedia.com/salestools/MHAN-7ESBDV_R0_EN.pdf