Building Wiring Fault light

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Building Wiring Fault light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
5
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

Building Wiring Fault light

I have an APC Smart-UPS Online UPS (APC SMART-UPS RT 1500VA 120V Tower, SURTA1500XL).

I also have a spare rackmounted APC surge protector (APC Black Rackmount SurgeArrest 9 Outlet 120V, NET9RMBLK) to which some switches are connected.

When I connect the surge protector to one of the outlets on the UPS, the red "Building Wiring Fault" light on the surge protector is lit.

However, when I connect the surge protector directly to one of the wall outlets, the red "Building Wiring Fault" light goes away.


1> The UPS is grounded for sure and there is no wiring fault light on the UPS itself, so why would the surge protector (which is connected to the outlets on the UPS) indicate that there is a wiring fault?

2> Is that a real wiring fault that I should be concerned about? Is the surge protector (which is connected to the UPS) still grounded and still offer the necessary surge protection for devices connected to it?


One may question why I have it set up that way. The reason I am connecting the rackmounted surge protector to a UPS is because I cannot afford to buy another PDU for now and because of the limitations of the lengths of the existing power cords. The surge protector is the only one that could reach that far, so I am using it as a poor man's PDU of a sort.

And no, I cannot move the UPS and the switches any closer to one another.

Is there any down side to doing it this way? Is that wiring fault light on the surge protector a real concern?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

I received a power conditioner with the BWF on. I plugged it into an APC surge protector with a BWF and the light on the surge protector is not lit, but the light on the power condition is still lit. This tells me I received a defective power conditioner.

Any idea how I can fix it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

Hi clarkson,

The wiring fault LED on the surge protector always lights up when plugged into the UPS.

I had also tried removing the surge protector from the rack and plugged it into a Smart-UPS 1000 in another closet, and the wiring fault LED on the surge protector also lit up.

The light went away whenever I plugged the surge protector directly to the wall though.


On a separate possibly unrelated note, the wiring fault LED (of the UPS unit itself) is not lit on either UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

Thanks. I don't have a voltmeter readily available, but I will try to find (or buy) one and get the measurements.

In this instance, what is the range of the AC voltage I should expect to see for Neutral-Ground on the receptacle? Just asking in case I get my hands on an older manual-ranging voltmeter or multimeter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

Hi clarkson,

I finally measured the AC voltage for the wall outlet, the receptacles on the SmartUPS RT 1500, the receptacles on the SmartUPS 1000. They are as followed:

1> Wall Receptacle:

Hot-Neutral: 121.8 V AC
Hot-Ground: 121.5 V AC
Neutral-Ground: Approximately 0.776 V

2> Smart-UPS 1000:

Receptacle # 1:

Hot-Neutral: 118.2 V
Hot-Ground: 119.7 V
Neutral-Ground: Between 1.864 V and 2.256 V

Receptacle # 2:

Hot-Neutral: 117.6 V
Hot-Ground: 119.7 V
Neutral-Ground: Between 1.739 V and 2.230 V


3> SmartUPS RT 1500

Receptacle # 1:

Hot-Neutral: 119.4 V
Hot-Ground: 121.5 V
Neutral-Ground: Between 0.619 V and 0.630 V

Receptacle # 2:

Hot-Neutral: 119.4 V
Hot-Ground: 121.5 V
Neutral-Ground: Between 0.820 V and 0.846 V


None of the Neutral-Ground voltage of the UPS outputs ever exceeded 2.5 V, so I'm not sure why that fault LED would light up when the suppressor is plugged into the UPS.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

Based on those voltage readings, is it still OK to leave the surge suppressor plugged into the UPS even with the Building Wiring Fault LED on? Will the switches connected to the surge suppressor still be protected? Or should I just plug the surge suppressor directly into the wall just to play it safe?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:40 AM

I received a power conditioner with the BWF on. I plugged it into an APC surge protector with a BWF and the light on the surge protector is not lit, but the light on the power condition is still lit. This tells me I received a defective power conditioner.

Any idea how I can fix it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore