Brand new Smart-UPS X 3000 showing errors /discharged battery
![]() |
The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. |
![]() |
Compensating for a high input voltage. |
From status:
|
|||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
UPS is working, but battery doesn't seem to be getting a charge, not sure how to fix.
thanks
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 05:56 AM . Last Modified: 2024-03-18 03:00 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:56 AM . Last Modified: 2024-03-18 03:00 AM
it must have just been needing a good charge. Checked this morning and its "online' and green.
The unit was brand new to me, but must have been sitting in some stockroom for years. MFG on battery is 2014. Its charged 100% now though.
thanks
Sean
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:56 AM . Last Modified: 2024-03-18 03:00 AM
The float voltage of your battery is currently 136v, so it is definitely getting a charge. I see in your title that the unit is new. Do you have the serial number? Also - Have you adjusted the low battery signal time from the factory defaults?
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 05:56 AM . Last Modified: 2024-03-18 03:00 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:56 AM . Last Modified: 2024-03-18 03:00 AM
it must have just been needing a good charge. Checked this morning and its "online' and green.
The unit was brand new to me, but must have been sitting in some stockroom for years. MFG on battery is 2014. Its charged 100% now though.
thanks
Sean