Brand New APC Smart-UPS SRT10K Management Card will not take IP address

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Brand New APC Smart-UPS SRT10K Management Card will not take IP address
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
1
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

Brand New APC Smart-UPS SRT10K Management Card will not take IP address

Hi,

We have recently taken delivery of a pair of new SRT10K UPS's.  One of the devices will not allow IP management since first trying to change it's IP.  When initially powered up it gained a standard DHCP address that we were able to use to get into the web management and begin configuring.  

We assigned it a new static IP and told the management card to reboot.   Since then it is refusing to set an IP.  On the screen on the front of the UPS it always lists 0.0.0.0 as its ip address,mask and gateway.  

Setting a manual IP on the screen says it is rebooting the management card but after waiting a couple of minutes the ip is still 0.0.0.0.  Setting it back to dhcp on the screen causes the same behaviour.

Any suggestions?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
0
1721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

Can you share the settings you're trying to set?

In case something you didn't notice got set improperly too, you could find the pinhole reset button on the back of the SRT's network management interface and hold it down with a paperclip or similar for 20+ seconds to re-configure/wipe ALL of the settings on the management interface and gives you a fresh start. (This is called a format.) During this process, if don't correctly, the status LED on the ethernet jack would "pulse" green and change to amber/orange when the operation is complete.

The only other thing that came to mind, specific to the default gateway showing 0.0.0.0 was this knowledge base -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA171016

If you didn't want to wipe the settings you already put on there, I'd want you to log in via serial connection and see what it is in the logs and what the tcpip command shows.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
0
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

Can you share the settings you're trying to set?

In case something you didn't notice got set improperly too, you could find the pinhole reset button on the back of the SRT's network management interface and hold it down with a paperclip or similar for 20+ seconds to re-configure/wipe ALL of the settings on the management interface and gives you a fresh start. (This is called a format.) During this process, if don't correctly, the status LED on the ethernet jack would "pulse" green and change to amber/orange when the operation is complete.

The only other thing that came to mind, specific to the default gateway showing 0.0.0.0 was this knowledge base -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA171016

If you didn't want to wipe the settings you already put on there, I'd want you to log in via serial connection and see what it is in the logs and what the tcpip command shows.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore