Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Battery life

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery life
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
ianh21
ianh21
Cadet

Posted: ‎2024-09-18 01:53 AM

0 Likes
3
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 01:53 AM

Battery life

Hi

 

I have 14 x APC by Schneider Electric Smart-UPS SMT-SmartConnect - SMT750IC - Uninterruptible Power Supply 750VA (Cloud enabled, 6 Outlets IEC-C13)  in my unit that are new and open box.  the batteries and testing by yourselves was conducted in 2018. 

As they have not been used, will the batteries be fine still?

 

how long do they last if the units are brand new unused?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-09-18 03:21 AM

0 Likes
1
816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 03:21 AM

The service life of the battery cartridge is rated for 2-5 years based on usage, temperature, and environmental conditions.

 

If these units were NOS and left to sit on the shelf uncharged for six years. You’ll need to inspect all the battery cartridges for any physical damage such as swelling, bulging, leakage, etc.

 

If no physical damage is found you may proceed to do some basic voltage tests. Take any cartridge that hasn’t been charged and document what the resting voltage is.

 

A new cartridge depending upon how long it was allowed to sit on the shelf will span 12.80 ~ 13.XX (Per Cell).

 

The SMT is a 24 VDC battery system as such the testing voltage should be > 25.60 VDC.

 

The cells are rated to endure 260 full depletion cycles in normal situations. Afterwards the performance and operational service life begins to drastically decrease.

 

If you see any cartridge that is below 12 / 24 VDC set them aside as they are suspect. To know the true health of the individual battery cells you must measure the internal resistance of the cell and compare it to the battery manufacturers specification sheet.

 

This is done with a specialized conductance meter not a standard multimeter set to resistance / Ohms! ☝️

 

If this is a CSB battery it will be 20 mOhms. If they measure approximately 20 - 25 mOhms recharge the cartridge until the system indicates it’s 100% charged.

 

Let it sit like this for another 48 hours with the system float charging the cartridge. Afterwords disconnect the cartridge and measure the voltage it will show greater than 25 VDC.

 

Let the cartridge sit like this disconnected for at least 72 hours. Come back and measure the voltage. It should have lost no more than 0.1 ~ 0.5 VDC.

 

If the entire cartridge measures below < 24 VDC the battery cells need to be replaced. 

You can validate this simply by completing a battery calibration with at least 30% attached load. Compare the operational runtime to the APC Runtime Calculator for a given load / wattage.

 

If say the expected operational runtime is 60 minutes but you only see 5-10 minutes the batteries are toast!

 

If however you see 25~35+ minutes the battery cartridge is marginal. You can continue to use the cartridge knowing it can and will fail at some inopportune moment or order a replacement.

 

Complete the tests up above and report back your results and findings. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

ianh21
ianh21
Cadet

Posted: ‎2024-09-18 09:51 AM

In response to Teken
0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 09:51 AM

Thanks for your detailed reply.  These will not be tested by me as i do not have the time nor space.  I will sell them for parts only to clear. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2024-09-18 11:45 PM

0 Likes
0
768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 11:45 PM

Good Morning

Batteries left in units connected would discharge quicker, of the batteries was disconnected the batteries would self discharge faster.

Either way the batteries would sulfate, internally on the negative  pole, and once it crystalizes it is very difficult to recover the batteries. any recovery would have limited battery life if any. Its always better to leave unused UPS systems plugged in and charging its batteries. but in this case the batteries would be past its normal service life. In addition to the above procedure, you may tru to boost charge the batteries for 12 to 24 hours. See OEM guidance on boost charging. I don't think float charging will reverse the sulfate in the battery. Please let us know if you are able to recover the batteries. best of luck.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore