Battery disconnected = end of life? (after 6 years)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery disconnected = end of life? (after 6 years)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
6
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

Battery disconnected = end of life? (after 6 years)

hi there,

we have a SUA2200XLI running since 2011 (I'm working in this company since 6 months) and in the past nobody cared about it - it was always running well, so...... Since two days ago the UPS is beeping shortly every 5 sec. aprox  and the red light with the X inside the battery icon is flashing. battery level led's are off. sometimes it stops beeping and flashing and the battery charge leds are all green.... there was the powerchute installed on the server attached to the ups but the company who did the installation says there is no password (or better they lost it or won't give it to us....). I removed the old powerchute business edition and installed a new one, I wanted to know more before eventually replacing the batteries. powerchute says there are no batteries attached. Sometimes when the ups stops blinking and beeping the batteries are recognized as fully charged and battery voltage between 51 and 54 V.

So my question is: could this error (problem) be related to the battery that are at the end of life after 6 years? or should we consider a hardware failure?

thank you in advance for your help

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • battery
  • beeping
  • hardware
  • PowerChute
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:41 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:41 AM

hi brad, thanks for explanation! I will try to change the batteries and hopefully get the ups working again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

Hi,

The description sounds like a battery issue however the battery voltage reading of 51 to 54 volts looks good. I suggest when time permits power down the attached load. Then hold the power on button for 5 to 6 seconds the prompt the UPS to run a self-test. if the test passes the batteries should be good. Another test you can run is with the attached load powered off plug a lamp into the UPS. Turn the lamp on and switch the UPS to battery by killing AC to it. Monitor the UPS to see if it will keep the lamp lit for a reasonable amount of time which will depend on the wattage draw of the bulb. 

If both of the test pass and the UPS continues to report disconnected battery then the issue is hardware. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

thanks bill, I will try to perform the two tests you suggested and see what happens.

thanks again, alex

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

Unfortunately at the moment I'm not able to perform the tests: the unit is continuously showing "batteries disconnected" - only sometimes the event log shows that the batteries were connected sometimes for a few seconds, sometimes for 1-2 minutes.....

I'm in real trouble, because we would like to avoid the purchase of 2 new batteries and have the same problems.

Any help or suggestion is really appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

The UPS dose not recognize the batteries anymore, if I unplug the batteries an measure the output voltage with a MM, one battery says 13,5 V and the other one 19,9 V. Can someone tell me if this is OK? I would really like to avoid the purchase of two new batteries and then find out that the UPS has a failure.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:42 AM

On 23/6/2017 3:54 PM, alex said:

one battery says 13,5 V and the other one 19,9 V

Unless I'm very much mistaken each of those "batteries" are a pair of 12V batteries taped together. Two of those blocks gives you ~48V nominal.

You should be seeing ~24V on each and thus I'd go out on a limb and say your batteries are toast and need replacing.

There are generally two failure modes of batteries.

A) They start to short internally, getting hot, swelling up and draging the UPS battery voltage down (so you can read that on the NMC). Sometimes you need to dismantle the UPS to get them out as they swell so much.

B) They lose plate material and develop a high resistance. The UPS thinks they are just fine as the float voltage sits right where it should be. You only know there's a problem if either the UPS runs a self test, or you lose power and notice the whole thing dies under load. High resistance batteries can intermittently show signs of failing self test.

The UPS has 2 tests for the battery. It frequently stops the charger and measures the battery voltage. It does this to detect the presence of the pack. A high resistance battery will often pass this test. The second test is the self test under load, where the ups tries to transfer onto battery. A high resistance battery *can* under some circumstances actually cause a load drop here as by the time the UPS figures the battery isn't going to cut the mustard, the load has already died before it can transfer back to mains. One to watch.

In your case it sounds like they've gone high resistance, and the standing test voltages confirm they're dead Jim.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:41 AM

0 Likes
0
2248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:09 AM . Last Modified: ‎2024-03-18 02:41 AM

hi brad, thanks for explanation! I will try to change the batteries and hopefully get the ups working again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore