Battery charger fault exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery charger fault exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

0 Likes
1
6033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

Battery charger fault exists

I have a few Smart-UPS rackmount RT 7500 XL systems that periodically give an error message after doing a self-test. The following is information on one of those 3 giving us the message.

On the home page Recent Device Events:
06/02/2009 07:02:13 UPS: A battery charger fault no longer exists.
06/02/2009 07:02:12 UPS: A battery charger fault exists.
06/02/2009 07:01:38 UPS: Passed a self-test.
06/02/2009 07:01:22 UPS: Started a self-test.

I get an e-mail for each event above. Here's the e-mail that is sent to me for the charger fault:


Name : APC3


Location : Stevens Point WI


Contact :Dave


[http://apc3.skyward.com/]


[http://10.1.1.163/]



Serial # : ZA0520016683


Device Ser #: YS0527121104


Date: 06/02/2009


Time: 07:02:13


Code: 0x012A



Critical - UPS: A battery charger fault exists.



About UPS
Model:Smart-UPS RT 7500 XL
Position:TOWER
Serial Number:YS0527121104
Firmware Revision:475.14.W
Manufacture Date:07/02/05

Hardware Factory
Model Number:AP9619
Serial Number:ZA0520016683
Hardware Revision:A10
Manufacture Date:05/14/2005
MAC Address:00 C0 B7 76 C7 C5
Management Uptime:57 Days 11 Hours 55 Minutes

Application Module
Name:sumx
Version:v3.5.7
Date:08/13/2008
Time:20:18:13

APC OS
Name:aos
Version:v3.6.1
Date:08/13/2008
Time:18:49:49


Below is the UPS status before a self test.
Status
Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:91.4°F
Runtime Remaining:20 minutes
Power
Input Voltage:210.2 VAC
Bypass Input Voltage:
Output Voltage:207.0 VAC
Current:
Input Frequency:60.00 Hz
Load
Load Power:54.0 %Watts
Apparent Load Power:44.0 %VA
Load Current:15.86 Amps
Battery
Capacity:100.0 %
Battery Voltage:214.9 VDC
External Batteries:1

And below is the status after a self test is performed.

Status
Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:91.4°F
Runtime Remaining:13 minutes
Power
Input Voltage:208.8 VAC
Bypass Input Voltage:
Output Voltage:208.2 VAC
Current:
Input Frequency:59.99 Hz
Load
Load Power:54.0 % Watts
Apparent Load Power:43.0 %VA
Load Current:15.86 Amps
Battery
Capacity:69.0 %
Battery Voltage:218.1 VDC
External Batteries:1


The battery capacity drops to 69% in the short amount of time the self test is performed. I did not get a charge failure message on it this time.
These batteries were replaced about a month ago and we were recieving these charge failures before the batteries were replaced.
Any help would be appreciated.
Thanks,
Dave

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

0 Likes
0
6033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

The battery charger fault is unfortunately not a "fixable" error in the longterm, so if you have been getting it consistently I would call into APC Tech Support and check on your warranty status on the units affected. Based on a quick glance, the unit below is not in warranty, but T.S. will be able to check on extended warranties, etc. etc.

It is possible that you will get some more life out of the units without having them replaced, as this fault does not always mean that the batteries will not be recharged. But, if you are supporting anything you consider important with the RT units I would look into having them replaced via warranty or "trading up."

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

0 Likes
0
6034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:18 PM . Last Modified: ‎2024-03-14 04:39 AM

The battery charger fault is unfortunately not a "fixable" error in the longterm, so if you have been getting it consistently I would call into APC Tech Support and check on your warranty status on the units affected. Based on a quick glance, the unit below is not in warranty, but T.S. will be able to check on extended warranties, etc. etc.

It is possible that you will get some more life out of the units without having them replaced, as this fault does not always mean that the batteries will not be recharged. But, if you are supporting anything you consider important with the RT units I would look into having them replaced via warranty or "trading up."

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore