Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
Good morning.
Recently I bought a rack automatic transfer switch ATS 7724. We have connected both UPS to both inputs: A and B.
I have only voltage in the outputs of the BANK 1 16A, but not the BANK 2.
Could someone help me?
Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
First thing to do is check the status of the breaker for Bank 2.
Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.
http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
First thing to do is check the status of the breaker for Bank 2.
Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.
http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.