Good morning.
Recently I bought a rack automatic transfer switch ATS 7724. We have connected both UPS to both inputs: A and B.
I have only voltage in the outputs of the BANK 1 16A, but not the BANK 2.
Could someone help me?
Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
First thing to do is check the status of the breaker for Bank 2.
Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.
http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:02 AM . Last Modified: 2024-03-18 12:57 AM
First thing to do is check the status of the breaker for Bank 2.
Please review this document below and try full tripping the breaker and resetting it. Or let us know if the breaker is damaged.
http://www.apcmedia.com/salestools/ASTE-6Z6K8Q/ASTE-6Z6K8Q_R0_EN.pdf