Bad batteries or not charging?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Bad batteries or not charging?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:27 AM . Last Modified: ‎2024-03-17 11:17 PM

0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:27 AM . Last Modified: ‎2024-03-17 11:17 PM

Bad batteries or not charging?

Smart UPS SC-1500

UPS Status
- System Status
Device StatusOn Line, Battery Discharged
UPS Load18.2%
Runtime Remaining0Minutes
Internal Temperature2.0°C / 35.6°F
- Power Status
Input Voltage123.0VAC
Output Voltage123.0VAC
Input Frequency60.0Hz
Output Frequency60.0Hz
- Battery Status
Battery Charge100.0%
Battery Voltage26.9VDC
What is going on?  We have no runtime available despite no outages for some time.  The UPS also triggered a shutdown on 12-15 with supposedly no outage?  
Data log over that time:
12/15/18 10:41:18 124.0 124.0 26.9 100 60.0 60.0 14.3 2.0
12/15/18 10:21:18 124.0 124.0 26.9 100 60.0 60.0 14.9 2.0
12/15/18 10:01:18 124.0 124.0 26.9 100 60.0 60.0 14.9 2.0
12/15/18 09:41:18 124.0 124.0 26.9 100 60.0 60.0 14.3 2.0
12/15/18 09:21:18 124.0 124.0 26.9 100 60.0 60.0 14.9 2.0
12/15/18 09:01:18 124.0 124.0 26.9 97 60.0 60.0 14.9 2.0
12/15/18 08:41:18 124.0 124.0 26.9 94 60.0 60.0 14.3 2.0
12/15/18 08:26:02 124.0 124.0 26.9 100 60.0 60.0 18.2 2.0
12/15/18 08:06:02 124.0 124.0 26.9 100 60.0 60.0 17.5 2.0
12/15/18 07:46:02 124.0 124.0 26.9 100 60.0 60.0 17.5 2.0
Event log: 
12/15/18 21:01:29 Battery Discharged
12/15/18 21:01:28 Self Test Passed
12/15/18 21:01:16 Self Test Initiated
12/15/18 21:01:16 Battery Charge in Range
12/15/18 21:00:55 Battery Discharged
12/15/18 21:00:55 Calibration Complete
12/15/18 21:00:50 Calibration Started
12/15/18 21:00:49 Battery Charge in Range
12/15/18 08:41:01 Insufficient Runtime Available
12/15/18 08:40:59 Battery Discharged
12/15/18 08:40:58 Communication Established
12/15/18 08:40:44 Monitoring Started
12/15/18 08:27:18 Monitoring Stopped
12/15/18 08:27:17 Main Group commanded to: shutdown using delay
12/15/18 08:27:17 Low Runtime Remaining
12/15/18 08:27:17 Shutdown process started
12/15/18 08:27:16 Low Battery
12/15/18 08:27:16 On Battery
12/14/18 22:25:44 Insufficient Runtime Available
12/14/18 22:25:42 Battery Discharged
12/14/18 22:25:42 Communication Established
12/14/18 22:25:27 Monitoring Started
12/14/18 21:45:05 Monitoring Stopped
12/9/18 09:45:41 Insufficient Runtime Available
12/9/18 09:45:39 Battery Discharged
12/9/18 09:45:39 Communication Established
12/9/18 09:45:23 Monitoring Started
12/9/18 09:07:45 Monitoring Stopped
Is the unit itself bad?  These batteries are less than 2 months old, and are standard replacement batteries.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of