I have 3 Backup UPS systems reporting 360+ minutes of battery time. These have one regular tower and maybe a monitor. The box on the 550G said 43 minutes.
Anyone had a similar issue? a solution ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:00 AM . Last Modified: 2024-03-13 12:11 AM
Hi , thanks !!!! I have a PC/ monitor and small thermal printer on a 550, and a PC and 8 port switch on a 700
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:59 AM . Last Modified: 2024-03-13 12:11 AM
Sounds like your load is exceptionally low. I wouldn't worry about it. I am not sure about this particular system, but you may be able to do a run-time calibration test to check it out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:59 AM . Last Modified: 2024-03-13 12:11 AM
Hello Chris,
Good day to you. Joe is correct, the runtime of the UPS showing in powerchute might be inaccurate due to low load. At least 30% load should give you a much better runtime. May I know how much load is connected to the UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:00 AM . Last Modified: 2024-03-13 12:11 AM
Hi , thanks !!!! I have a PC/ monitor and small thermal printer on a 550, and a PC and 8 port switch on a 700
Link copied. Please paste this link to share this article on your social media post.