The runtime on a new battery with 150W load indicates 10minutes. With no load it indicates 85-89 minutes or so.
I don't have a PC, how do I set the date? My prior battery installed in 2023 started beeping at me incessantly, and I probably replaced it too soon due to the run time.
APC BR1500G #124 battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-08 08:48 AM
Your options are limited to using a Windows / Linux computer running APC PCSS and connecting to the UPS.
Other possible methods are to use a VM / Parallels to mimic a Windows environment. Regardless of the battery installation date you’ll need to complete the following action items onward:
Self Test: Manually initiate a self test and let pass and wait for the RBC to recover to 100% SOC (State of Charge).
Calibration: Manually initiate a battery calibration with a minimum of 30% attached load or greater. Once complete allow the RBC to recover and return to 100% SOC.
This will allow the system to more accurately reflect the operational runtime of the new RBC via the LCD, Power Chute, NUT, etc.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-08 08:48 AM
Your options are limited to using a Windows / Linux computer running APC PCSS and connecting to the UPS.
Other possible methods are to use a VM / Parallels to mimic a Windows environment. Regardless of the battery installation date you’ll need to complete the following action items onward:
Self Test: Manually initiate a self test and let pass and wait for the RBC to recover to 100% SOC (State of Charge).
Calibration: Manually initiate a battery calibration with a minimum of 30% attached load or greater. Once complete allow the RBC to recover and return to 100% SOC.
This will allow the system to more accurately reflect the operational runtime of the new RBC via the LCD, Power Chute, NUT, etc.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-09 09:31 AM
Thanks. I can download Linux, I think Windows needs to purchase a license. Where can I find the software for Linux?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-10 03:41 AM
The only requirement to download PCSS application is creating a APC / Schneider account.
You may use this resource link to download a copy of APC Power Chute (PCSS) where it say’s compatible software once you’ve created an account:
Questions Ask . . . 👍