Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Available runtime has been exceeded.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Available runtime has been exceeded.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

0 Likes
3
3022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

Available runtime has been exceeded.

Good morning

I am trying to configure PCNS to shutdown my VMs gracefully and am getting confused.  Using PMAR-9DNLQK_R4_EN.pdf as source material.

I overspec'd the UPS by adding an extra battery and have around 7 hours of Runtime Remaining:

4Yf7JhrZ9snqXAZ0o6QkpQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png4Yf7JhrZ9snqXAZ0o6QkpQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

NMC version: 6.5.6
PCNS version: 4.3 (running on vCenter)

I have set the Low Battery Duration (NMC) to 10 minutes.  This I believe is the estimated time before the battery becomes depleted.

In PCNS (in Virtualization Settings) the Virtual Machine and Virtual Appliance, Shutdown and Startup Shutdown Duration is set at 120 seconds.  Is this figure per VM (I have 13) or all VMs?

Page 33 states "The Duration field is the time allowed for all the VMs/vApps to gracefully shut down", which would indicate that this is for all VMs and vApps.  With these settings PCNS reports an "Available runtime has been exceeded" erorr.

Condition 3 of https://www.apc.com/us/en/faqs/FA241713/ seems to apply to my scenario and states as a solution:
"Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute", but if the VM Shutdown Duration for all VMs is 2 minutes and the vCenter Server VM Shutdown Duration is 4 minutes then the Low Battery Duration has 4 minutes to spare (if I'm correct!)

Am I missing something?

Tony

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:05 AM . Last Modified: ‎2024-02-14 11:32 PM

0 Likes
0
3021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:05 AM . Last Modified: ‎2024-02-14 11:32 PM

Hi,

On 11/6/2019 6:22 AM, Tony said:

Why am I getting the "Available runtime has been exceeded" error?

The warning is posted because runtime has been exceeded take into account VM/vApp shutdown delay, vCenter shutdown delay, VM/vApp startup duration, 2 minutes for OS shutdown command delay, and an additional 2 minutes. So, with your configuration the low battery duration should be a minimum of 12 minutes to clear the warning. 

There is a diagram on page 105 of the User's Guide that shows the process. The diagram shows 70 second delay for OS shutdown command and that is rounded up to 2 minutes. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

0 Likes
0
3021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

Hi,

10 minutes is the minimum and would be sufficient base on VM and vCenter shut down durations of 6 minutes. Did you configure VM migration, VM start-up or have you configured prioritization. Those number will affect the time needed to safely power down and trigger the warning. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

0 Likes
0
3021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:04 AM . Last Modified: ‎2024-02-14 11:32 PM

Thanks Bill,

Migration hasn't been configured, but VM start-up is enabled an the default value.

Why am I getting the "Available runtime has been exceeded" error?

Tony

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 01:05 AM . Last Modified: ‎2024-02-14 11:32 PM

0 Likes
0
3022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 01:05 AM . Last Modified: ‎2024-02-14 11:32 PM

Hi,

On 11/6/2019 6:22 AM, Tony said:

Why am I getting the "Available runtime has been exceeded" error?

The warning is posted because runtime has been exceeded take into account VM/vApp shutdown delay, vCenter shutdown delay, VM/vApp startup duration, 2 minutes for OS shutdown command delay, and an additional 2 minutes. So, with your configuration the low battery duration should be a minimum of 12 minutes to clear the warning. 

There is a diagram on page 105 of the User's Guide that shows the process. The diagram shows 70 second delay for OS shutdown command and that is rounded up to 2 minutes. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of