APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 07:09 AM . Last Modified: 2024-03-12 04:42 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2024-03-12 04:42 AM
Scenario...
APC750 (SMT750RMI2U) is located in a fairly remote location.
We recently lost primary power to the space and the batteries ran dead.
Once the normal primary power was restored, the APC 750 had to be "manually" turned back on.
This is quite inconvenient due to the driving distance from the main office.
Is there a setting in this APC device that will automatically initialize the device upon restoration
of regular primary power?
Thanks in advance.
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2024-03-12 04:42 AM
If the UPS turns off due to a low battery (with no intervention from software via USB or serial or a UPS Network Management Card), then it should turn back on automatically when AC power is restored.
Let's start here - do you have PowerChute Business Edition in use via serial/USB or is there a UPS Network Management Card installed in this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2024-03-12 04:42 AM
If the UPS turns off due to a low battery (with no intervention from software via USB or serial or a UPS Network Management Card), then it should turn back on automatically when AC power is restored.
Let's start here - do you have PowerChute Business Edition in use via serial/USB or is there a UPS Network Management Card installed in this UPS?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.