Appropriate PDU for L6-30-R 250V plug
  • Appropriate PDU for L6-30-R 250V plug
Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-18 03:20 AM
936
I have a plug in my machine room thats listed as 'L6-30-R 250V'.
I can't seem to find any PDU's that have an input voltage of 250V. Can I plug a PDU with a smaller input voltage into this, assuming the PDU has an L6-30 plug on it?
any APC Rack PDU that you see that has an L6-30P on it can support 208v or 240v nominal voltage so you can look at any PDU with an L6-30P on it that APC spports. you'll see in the technical specifications sheet for each product..
Input connector - NEMA L6-30 plug
Nominal input voltage - 200 – 240 VAC
Acceptable input voltage - ± 10% of nominal voltage
you just want to make sure that you are using the proper configuration - such as hot, hot, ground or hot, neutral, ground depending on what part of the world you are in.