I have a plug in my machine room thats listed as 'L6-30-R 250V'.
I can't seem to find any PDU's that have an input voltage of 250V. Can I plug a PDU with a smaller input voltage into this, assuming the PDU has an L6-30 plug on it?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:29 AM . Last Modified: 2024-03-18 03:20 AM
any APC Rack PDU that you see that has an L6-30P on it can support 208v or 240v nominal voltage so you can look at any PDU with an L6-30P on it that APC spports. you'll see in the technical specifications sheet for each product..
Input connector - NEMA L6-30 plug
Nominal input voltage - 200 – 240 VAC
Acceptable input voltage - ± 10% of nominal voltage
you just want to make sure that you are using the proper configuration - such as hot, hot, ground or hot, neutral, ground depending on what part of the world you are in.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:29 AM . Last Modified: 2024-03-18 03:20 AM
any APC Rack PDU that you see that has an L6-30P on it can support 208v or 240v nominal voltage so you can look at any PDU with an L6-30P on it that APC spports. you'll see in the technical specifications sheet for each product..
Input connector - NEMA L6-30 plug
Nominal input voltage - 200 – 240 VAC
Acceptable input voltage - ± 10% of nominal voltage
you just want to make sure that you are using the proper configuration - such as hot, hot, ground or hot, neutral, ground depending on what part of the world you are in.