Application API putting computer in sleep mode. No "On Battery" event shown.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2901:26 AM. Last Modified: 2024-03-1305:34 AM
Application API putting computer in sleep mode. No "On Battery" event shown.
After weekend, Computer was off, had to manually power it on. Once started, taking a look on PowerChute, it show no events happened.
Looking in Windows Event Viewer..
Source: APC Data Service - ID: 0 PowerEvent handled successfully by the service.
Then on the following second..
Source: Kernel-Power - ID: 42 The system entering sleep. Sleep Reason: Application API
PCPE is set to turn off computer once it reach 5 mins left on battery only. The battery is supposed to be able to support it for 2 hours (so it should not be a "short duration" event).
I'm starting to doupt if it really lost power or if something else did happen. There is no other APC event logged in event viewer before that time during the day.
This Post concern: Back-UPS RS 1500G with an external battery pack.
Any way to get more details about that "PowerEvent"?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2901:26 AM. Last Modified: 2024-03-1305:34 AM
David,
On 12/7/2015 12:11 PM, David said:
Any way to get more details about that "PowerEvent"?
Unfortunately no. I suggest testing the UPS. Power down the computer and plug a lamp into one of the UPS battery outlets. Then put the UPS on battery to see if it will support the lamp. To put the UPS on battery it is best to have the UPS plugged into a power strip and turn the strip off. If you unplug the UPS from an outlet you are removing ground and in some cases a UPS will not react as designed. If the lamp stays on then run the same test but this time have the computer powered on and kill power to the UPS to see how PowerChute handles the event.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2901:26 AM. Last Modified: 2024-03-1305:34 AM
David,
On 12/7/2015 12:11 PM, David said:
Any way to get more details about that "PowerEvent"?
Unfortunately no. I suggest testing the UPS. Power down the computer and plug a lamp into one of the UPS battery outlets. Then put the UPS on battery to see if it will support the lamp. To put the UPS on battery it is best to have the UPS plugged into a power strip and turn the strip off. If you unplug the UPS from an outlet you are removing ground and in some cases a UPS will not react as designed. If the lamp stays on then run the same test but this time have the computer powered on and kill power to the UPS to see how PowerChute handles the event.