Another Remote Power Off/ON Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Another Remote Power Off/ON Question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
7
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Another Remote Power Off/ON Question

After reading through many posts, I'm not 100% confident I've found a valid answer. I have (2) SPC SMART UPS 3000 units. I would like to be able to remotely poweroff and poweron the UPS themselves. My intent is to save the batteries. The equipment is used maybe 2-3 days per week and when it's not being used, people forget to go to the UPS and power it off. The batteries wind up dying in no time and then need replacement. I want to put physical switches in a location that people can see and is easy to get to so they remember to power off the UPS. It looks like the DB9 connector with shorts of 7-9 for ON and 7-8 for OFF would work, but then I read about the "vampire" situation. It also sounds like after 10 minutes of being powered off, the unit becomes braindead and can't be remotely powered on. Any way around any of this confusion?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Here is what I have:

Remote On/Off Control

DB9 – Turn On/Off

Remote On

Application of a short (or a momentary button) connected between pins 7 and 8 of the DB9 for 200 ms (60Hz) 240ms (50Hz) will result in the UPS detecting an ON command.  The UPS will then process its on sequence.

Remote Off

Application of a short (or a momentary button) connected between pins 7 and 9 of the DB9 for 200 ms (60Hz) 240ms (50Hz) will result in the UPS detecting an OFF command.  The UPS will then turn off immediately.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Here are my personal comments.

1.) If the UPS is off with the batteries still connected internally, they'd still be susceptible to discharging in the UPS since when the UPS is powered off, the charger is inactive and not maintaining a float charge on the batteries. That is why we always recommend you disconnect the batteries when storing your UPS for any amount of time to be safe. Your comment regarding how the batteries die in no time made me want to understand why and ask more questions because with little to no use (no deep discharges and just light use for a couple of transfers to batteries) in a situation like this, I would think you are definitely getting 3-5 years battery life. What are you actually seeing for a lifespan? When the UPS is powered up the 2-3 days a week, what kind of use are the UPSs seeing? Just powering the equipment and no transfers to battery?

2.) You're right - without AC power, the UPS will go "braindead" in 8-10 minutes. This means no power to the serial port. Before you'd be able to do anything with it, you need to restore AC power to it and then it would come back alive (the electronics become energized) and you could command the output back on or just push the power button. (A Network Management Card is also an option to remotely log in and command the output on).

My thought also is a UPS is designed to remain on most of the time and the vampire current will power the internal UPS electronics and help keep the batteries at float charge which should be minimal if they are not discharged often.

Also, for any further response or comments, could you provide the exact model of the UPS from the back of the UPS so we can ensure the comments made above are 100% accurate? Sounds like you have something like SUA3000RM2U or similar.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Very good and valid comments/questions Angela.

1. I think there are small units that are connected to the UPS system that most people aren't paying attention to that continue to drain the batteries (almost hidden within the racks). There are generally no transfers to battery only situations, but when people are done using the racked equipment, sometimes the AC is disconnected from the area. Although the majority of the equipment is off, there is still those few pieces here and there that aren't paid attention to.

2. If I can ensure the AC power remains constant, I shouldn't have to worry about the "braindead" state right? So I should still be able to use the DB9 based switching system for powerup?

It's going to take a few minutes for me to get to the back of the UPS and see exact model, but I think your correct with SUA3000RM2U. I'll verify and reply again with exact info.
""

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Ok, I'll wait for the model number.

Regarding # 1 - do you mean while the UPS is on battery, they drain the battery power? If the UPS is running online yet the hidden equipment is not being watched, it should not be draining the batteries unless the UPS is operating on battery power. (So I am still a little confused here).

Regarding # 2 - yes, you are correct. You can just keep the power output off on the UPS if you'd like and it'd keep charging the battery as needed and remain alive. And yes, you can use the DB-9 port since the UPS will be alive.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM


I can only see half the model number, but I do see SUA3000.

Yes, when the AC has been removed, people leave things plugged in drawing current and don't shutdown the UPS. I'll work to ensure that AC is kept constant. Can you just verify for me that my 7-8 is OFF and 7-9 is ON for the DB9?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

embarassed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:24 PM

Here is what I have:

Remote On/Off Control

DB9 – Turn On/Off

Remote On

Application of a short (or a momentary button) connected between pins 7 and 8 of the DB9 for 200 ms (60Hz) 240ms (50Hz) will result in the UPS detecting an ON command.  The UPS will then process its on sequence.

Remote Off

Application of a short (or a momentary button) connected between pins 7 and 9 of the DB9 for 200 ms (60Hz) 240ms (50Hz) will result in the UPS detecting an OFF command.  The UPS will then turn off immediately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-12 11:24 PM

0 Likes
0
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-12 11:24 PM

Perfect! Thanks so much for your help Angela. Based on everything I had read so far, I figured it would be you that would answer this for me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore