Alarm: Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Alarm: Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
3
3918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Alarm: Local Management-To-NMC Integrated EM Sensor Communication Lost: Universal I/O at Port 1

After updating our Firmware to V6.4.0 we're now getting the alarm in the subject line. Resetting only the "Lost Environment Communications Alarms" and rebooting the Management Interface have no affect. Looking in the Event Log, the error only occurs when the interface is rebooted. (IPs taken out, but are present)

 08/18/2016 08:59:44 Device Environment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 08/18/2016 08:59:43 Device Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 08/18/2016 08:59:41 System Network service started. IPv6 address x.x.x.x assigned by link-local autoconfiguration.
 08/18/2016 08:59:39 System Network service started. System IP is x.x.x.x from manually configured settings.
 08/18/2016 08:59:33 System Network Interface restarted.
 08/18/2016 08:59:25 admin Network Interface restarting. Web user request.

System info is as follows:

Hardware Factory

Model Number: AP8941
Hardware Revision: 02
Network Management Card
Model Number: AP9537
Hardware Revision: 05
Application Module
Name: sumx
Version: v6.4.0
APC OS (AOS)
Name: aos
Version: v6.4.0
APC Boot Monitor
Name: bootmon
Version: v1.0.8
 

This system is in production so taking it offline will require some coordination.

 

Any help is appreciated.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap8941
  • ap9537
  • lost-comm
  • universal-io
  • v6.4.0
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
3919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

Hi Ben,

The 0W05545A is referred to as a CAN bus terminator which is OK to have plugged into the in or out port. You use it specifically when you're utilizing our Network Port Sharing feature which physically connects up to 4 of these AP8XXX series Rack PDUs together over the CAN bus and you can share one IP address across all of them. The terminator gets moved to the beginning and end of your chain you create when doing this so we include a terminator with each PDU so that if you decide to use this feature, you have some available. Also, specifically, a few of the models, AP86XX and AP84XX I think too which offer metering by outlet functionality require the terminators to remain in or else a singular PDU of those types won't work properly. Your model doesn't require it for singular operation technically but you should leave it there as to not misplace it cool

Here is what I'd do if you can - is it possible to downgrade the one PDU one revision to see if the error still comes about? I can provide this firmware for you if you're willing. I am thinking it is either a coincidence that there is a problem with the UIO port #1 (or something damaged it around the same time) or there is a firmware issue we'd investigate further.

I would say if we downgrade the firmware, and still see the issue, then you may want to live with it if you don't use that port (supports a AP9335T temp or AP9335TH temp humidity sensor). We could also try a sensor in that port to see if it actually works or not regardless of what the error message is telling us, which is the on board management interface lost communication with that port - if you had one from a different product - NetBotz, UPS Network Card, etc. Or, if it sticks around no matter what firmware is loaded and you don't want to live with it (which I'd expect it to show after each reboot), then the display module could be replaced - either at your cost or not sure of your warranty on this one.

Let me know what you think or if you have questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
3919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Hi Ben,

Can you share the full event.txt file? You can export it from the web interface using the little floppy disk icon when you're viewing the event log.

Is anything physically connected to the Universal I/O port on the PDU? From an overall perspective, is there anything else besides a network cable connected to the display module on the PDU? And if so, what port is it in?

It is normal after the reboot to have 5-6 status messages like established communication with UIO port 1 but of course it shouldn't be telling you "lost communication" afterwards. I'd like to just see the full event log and see if anything else catches my eye and then hopefully you can tell me what is plugged in where, if anything.

What firmware did you have on prior? You're saying that you didn't see these types of messages before you upgraded the firmware?

Again, in the big picture, is this a single PDU showing this behavior or did you upgrade multiple units and just this one is showing an issue, even though others are setup the same way?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
3919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

Event file attached.

On the PDU we have a network cable and I don't know if it's some sort of loopback or just a protector, but it is similar to the link below. It's in the "Out" port of the PDU. I've rebooted the Network interface with and without that plugged in, no difference there.

Part #0W05545A

http://www.pdlglobal.com/data/product_images/1733_main_image.jpg 

Looking at the entire Event Log now, after upgrading the firmware we couldn't log back into the system, our network engineer had to go and reconfigure as you can see. Could this be some sort of configuration issue then?

I can't say what firmware version we had before, we're good at keep everything up to date, so I'd like to say it was the previously released version.

We have multiple PDUs at varies locations, we were able to upgrade them all no problem, this is our only problem child. And yes, they would all be configure the same.

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
3920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:18 AM

Hi Ben,

The 0W05545A is referred to as a CAN bus terminator which is OK to have plugged into the in or out port. You use it specifically when you're utilizing our Network Port Sharing feature which physically connects up to 4 of these AP8XXX series Rack PDUs together over the CAN bus and you can share one IP address across all of them. The terminator gets moved to the beginning and end of your chain you create when doing this so we include a terminator with each PDU so that if you decide to use this feature, you have some available. Also, specifically, a few of the models, AP86XX and AP84XX I think too which offer metering by outlet functionality require the terminators to remain in or else a singular PDU of those types won't work properly. Your model doesn't require it for singular operation technically but you should leave it there as to not misplace it cool

Here is what I'd do if you can - is it possible to downgrade the one PDU one revision to see if the error still comes about? I can provide this firmware for you if you're willing. I am thinking it is either a coincidence that there is a problem with the UIO port #1 (or something damaged it around the same time) or there is a firmware issue we'd investigate further.

I would say if we downgrade the firmware, and still see the issue, then you may want to live with it if you don't use that port (supports a AP9335T temp or AP9335TH temp humidity sensor). We could also try a sensor in that port to see if it actually works or not regardless of what the error message is telling us, which is the on board management interface lost communication with that port - if you had one from a different product - NetBotz, UPS Network Card, etc. Or, if it sticks around no matter what firmware is loaded and you don't want to live with it (which I'd expect it to show after each reboot), then the display module could be replaced - either at your cost or not sure of your warranty on this one.

Let me know what you think or if you have questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore