Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Agent Software unable to communicate with UPS-Network-Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Agent Software unable to communicate with UPS-Network-Card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
4
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Agent Software unable to communicate with UPS-Network-Card

Hi,
I´m using a Smart-UPS X 2000 with the following Network Card: AP9631.
Currently i´m trying to set up the PowerChute Agent software on some Clients (VirtualMachines).
I was able to install the software, and run the webinterface for configuration. (on a Windows and a Linux Machine)
After i configured everything according to this Video "https://www.youtube.com/watch?v=GLjvcB7IRCk&t=2s" , my Client (Agent) is unable to connect to the UPS-Network-Card.... (find screenshot)

Any ideas on how to troubleshoot?

Thanks and Best regards

Dustin

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

If your host/s are Citrix Xen we do not support installing on VMs. You will need to install on a standalone Windows or Linux server. See Schneider Electric FAQ FA159764. You will need the scripts to shut the host/s down. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

On 10/16/2018 10:51 AM, Dustin said:

Currently i´m trying to set up the PowerChute Agent software on some Clients (VirtualMachines).
I was able to install the software, and run the webinterface for configuration. (on a Windows and a Linux Machine)

We do not support installing PCNS on a Windows VM and only support PCNS running on PowerChute Linux VM for VMware or VMware vMA. The PowerChute VM is a CentOS Linux installed that is bundled with PCNS. VMware vMA is SuSE Linux and PCNS can be installed onto that. 

If the host/s are Windows Hyper-V we do not support installing on any VM. PCNS should be installed directly on the host. 

As for troubleshooting the communications please see Schneider Electric FA159624

The most common issues are mismatched use name, authentication phrase, subnet mask, or UDP port 3052 is blocked. When PCNS registers with the NMC it communicates over TCP port 80 or 443 and receives confirmation via UDP port 3052. As mentioned in the video the user name for PCNS client must match the set user name for PowerChute clients in the NMC. The authentication phrase must also match. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:08 AM . Last Modified: ‎2024-03-11 12:14 AM

On 10/16/2018 1:58 PM, Bill said:

If the host/s are Windows Hyper-V we do not support installing on any VM. PCNS should be installed directly on the host. 

Well maybe i'll start with, what i'm trying to do.

We are using a Xen-Server environment and for my first test i choose a Virtual Debian Machine from one of our Xen-Sever-Hosts.
I installed the PowerChute NetworkShutdown on this VirtualMachine (correct right?).

I want to configure this VM so that it will shutdown once the UPS is running on battery for 60 seconds (for testing).
Also i checked the ports on UPS and VM... 3052 is open on the VM but closed on the UPS (how do i open that?)

I´m going to make sure our configuration is correct once again.

Thanks in advance!
Dustin

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

Configuration seems fine

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:09 AM . Last Modified: ‎2024-03-11 12:14 AM

Hi,

If your host/s are Citrix Xen we do not support installing on VMs. You will need to install on a standalone Windows or Linux server. See Schneider Electric FAQ FA159764. You will need the scripts to shut the host/s down. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore