ATS network issues w/ Cisco 3750 switch

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS network issues w/ Cisco 3750 switch
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
127
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
7
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

ATS network issues w/ Cisco 3750 switch

Hi All,

We have around 20+ new ATS units to go in wiring closets. Most of our wiring closets have 3560's, 3750's, and 4506e's. We do not have ANY issues when the ATS is plugged into a 3560 or a 4506e, but when we plug ethernet into a 3750, the switchport keeps bouncing. This ONLY happens on a 3750 and we are running various versions of IOS, so I do not think that is the problem. I have also tried switching the port to AUTO, 100-Full, and 10-Full, but the port just keeps bouncing. I stumbled upon this in the alert logs ....

System: TCP/IP stack failure. Module: tfPacketChecksum-Data in Packet chain smaller than length to be checksumed

Has anyone seen this before?? Any ideas??

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

Hi All,

We have around 20+ new ATS units to go in wiring closets. Most of our wiring closets have 3560's, 3750's, and 4506e's. We do not have ANY issues when the ATS is plugged into a 3560 or a 4506e, but when we plug ethernet into a 3750, the switchport keeps bouncing. This ONLY happens on a 3750 and we are running various versions of IOS, so I do not think that is the problem. I have also tried switching the port to AUTO, 100-Full, and 10-Full, but the port just keeps bouncing. I stumbled upon this in the alert logs ....

System: TCP/IP stack failure. Module: tfPacketChecksum-Data in Packet chain smaller than length to be checksumed

Has anyone seen this before?? Any ideas??

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

Sorry, I should have included that in my original post. Event.txt is attached. Thanks for the help!!

Model Number: AP9617 - Hardware Revision: A10

Name: aos - Version: v2.6.4

Message was edited by: nmaxpierson

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

the AP9617 is just the network management card that is inside the ATS. I need the model of the actual ATS - it will be something like AP7750. you might need to physically look at the ATS or check in the network management card interface under Automatic Transfer Switch->Status->About ATS on the bottom of the page. let me know what that is but regardless, on the event log, it looks like you are on version 1.0.0 for NMC firmware. please verify AOS and APP version under Help->About in the web interface. you mentioned AOS is 2.6.4 - is that where you saw this info? I am not sure why the event.txt would say version 1.0.0 but you see 2.6.4 some place.

once you confirm that it is an APP (application module) of ats, we can upgrade the firmware to the latest. i can post it to this thread once we confirm.

thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

The unit is a AP7750. I have attached 2 screenshots, one under ATS -> Status and the other under Help -> About System which shows the AOS version.

Thanks again
M

Message was edited by: nmaxpierson

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

ok lets try this.

download your config.ini to save all of your configuration from the card (check these instructions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321]. then we will try a reset to defaults which i believe is under the system menu. ensure that you do NOT include your network settings.

then we can try to re-upload your config.ini file to see if the issue still exists. we could also try reseating the card inside of the ATS.

also another thing to try - can you try to disconnect the network cable from the card for about a half hour or so to see if maybe theres a packet on the network that the NMC doesnt like? you can try that first if its easier.

let me know how you make out.

also - you are using the latest rev of firmware so there is nothing to upgrade to.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:22 AM . Last Modified: ‎2024-03-18 03:35 AM

Ok, finally figured out what it was. Had nothing to do with any of the switches. Long story short, I have some devices (legacy) still on the network that affect other devices at times as they do a huge broadcast from time to time .... thus the error about ip stack error we saw in the console. Thanks to Mr. Wireshark, I was able to track down the issue. Moved to another vlan and issue resolved.

Thanks for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

no problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-18 03:35 AM

Hi All,

We have around 20+ new ATS units to go in wiring closets. Most of our wiring closets have 3560's, 3750's, and 4506e's. We do not have ANY issues when the ATS is plugged into a 3560 or a 4506e, but when we plug ethernet into a 3750, the switchport keeps bouncing. This ONLY happens on a 3750 and we are running various versions of IOS, so I do not think that is the problem. I have also tried switching the port to AUTO, 100-Full, and 10-Full, but the port just keeps bouncing. I stumbled upon this in the alert logs ....

System: TCP/IP stack failure. Module: tfPacketChecksum-Data in Packet chain smaller than length to be checksumed

Has anyone seen this before?? Any ideas??

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of