ATS failed to failover into Source B

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS failed to failover into Source B
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-02-14 10:11 PM

0 Likes
1
2935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-02-14 10:11 PM

ATS failed to failover into Source B

Hi all,

I got an issue on one of my ATS. Yesterday, our building was testing their power, and suddenly few servers had been rebooted.

Those servers are connected to the ATS, and there are two power source are connected to it.

One is from the building, and another one is from my UPS.

I checked inside the UPS, it's running low usage, and the battery is fine, all servers which connected to the UPS have no issue.

The problem is on the ATS. Then, I logged into the ATS and check, I found the following:

10/17/2016 18:18:00 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
10/17/2016 18:17:51 Automatic Transfer Switch: Fault cleared on Source A.
10/17/2016 18:17:44 Automatic Transfer Switch: Fault exists on Source A.
10/17/2016 18:17:27 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.

Source A which is from the building, and it failed to fail over to source B

Model Number: AP7721
Hardware Revision: 01

The ATS didn't reboot as well, the up time is over 180 days,

Anyone saw this issue before?

Thanks,

Edwin

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-01-29 11:38 PM

0 Likes
0
2935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-01-29 11:38 PM

Hello Edwin, 

I am sorry that you are having issues with your ATS. 

We do not do a lot of troubleshooting typically over forums, but I can give you a few thing to get you in the right direction. Please take a look at our k-base document FA156201. 

Also, we always recommend that both sources of the ATS be UPSs, since there can be short power blips. Also, what ATS do you have?

Thanks,
Shanon

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-01-29 11:38 PM

0 Likes
0
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:08 PM . Last Modified: ‎2024-01-29 11:38 PM

Hello Edwin, 

I am sorry that you are having issues with your ATS. 

We do not do a lot of troubleshooting typically over forums, but I can give you a few thing to get you in the right direction. Please take a look at our k-base document FA156201. 

Also, we always recommend that both sources of the ATS be UPSs, since there can be short power blips. Also, what ATS do you have?

Thanks,
Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login