ACRD 101 cooling unit issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRD 101 cooling unit issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 10:11 PM

0 Likes
18
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 10:11 PM

ACRD 101 cooling unit issue

Dear all,

I hope you will be fine. I am facing following issue in Inrow cooling unit of ACRD10. I need the your suggestion and support on this issue, Please do let me know, I will wait for your kind response.

Detailed logs are below mentioned.

APC | Data Log

Date  Time  Operate  Compressor  SupplyAir.C  ReturnAir.C  RackIn.C  Superheat.C  SctnTemp.C  SctnPresr.KPa  DschrgPresr.KPa  FilterDP.Pa  CoolDmd.kW  CoolOutput.kW  AirFlow.L/s  FanSpd.%  OHEInput  OHEOutput  HGBValvePos.% 

Regards

  • InRow RD 10KW: Compressor did not start exists.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acrd101
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

Thanks for your usual support

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:38 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:38 PM

Hello Muhammad. For this error, the compressor is not turning on when it is called for. A HVAC tech would need to check out the compressor to make sure it is good and also check the start capacitor to make sure it is the proper microfarad rating. Also check that the contactor for the compressor is getting the proper 208 volts to pull in. You can contract your local tech support to confirm the readings on the unit to help determine what is keeping the compressor from turning on. 

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

Dear Team,

I did the following steps...

  • Checked the compressor winding resistance about 2.1Ohm
  • Rating of capacitor which is looking good not physically swell.
  • Input at compressor contractor is 228V.
  • I have replaced th mother board with another running unit, that board is working good on this unit but is board is not working to any other unit.
  • Then i upgraded the updated firmware 0f 3.7.4

Will you please guide me how to check this board?

Will you guide me where is the option of SERVICE MODE so that i will be able to reset this mode? might be its service mode is enabled.

I will wait for your response.

Thank you for your kind cooperation.

Regards

MS

  • Tags:
  • acrd101
Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

Still waiting for your kind response.

Regards

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. When you checked the ohm readings on the compressor, what did you get from s-c, r-c and s-r? Was the contactor pulling in when the unit was calling for the compressor to run? Is the compressor getting hot at all?

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

I got the following readings

s-c=2.1Ohm

r-c=2.2Ohm

s-r=2.1Ohm

Motherboard is not sending the command to pull the contactor for the compressor to run, When compressor is not running then obviously it will not get hot.

I replaced the motherboard with other motherboard then this same unit is working fine.

Please guide me how to check motherboard, Is there any option of SERVICE MODE to reset the compressor command.

Please find the attached unit status report.

Your quick reply will be highly appreciable.

Regards

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

Dear team,

Can you share some kind of FSB or MOS documents.

 

Reagrds

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

Still waiting for your kind support

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. I am sorry about the delay. I would like to make sure, was it just the motherboard that was replaced or was it the motherboard with all the cards on the motherboard as well to get the unit working? I ask because the signal to turn on the compressor comes from the xa card that is connected to the motherboard in slot 1. If just replacing the motherboard caused the unit to run fine, then I would think we had a loose connections on one of the plugs. Check plug 12 and reseat the xa card (slot one on the old motherboard) to see if it was a loose connection. If all the cards were changed, try just swapping out the xa card (slot one) with the old one and see of the compressor will run. If it does not then the relay on the xa to turn on the compressor is bad. The xa card would need to be replaced. Unfortunately there is no service mode in these units to turn on the compressor manually.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

Hello...

Thank you for your prompt response. i got your highlighted points, i will visit couple of days to verify these points then will inform you with updates.

Regards

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

Dear Team,

Sorry for delay. Today i checked the unit as per your instruction,

  • I had replaced the xa card with other unit and check the connector plug J12. But there is no loose connection and there is no issue of xa card which is working fine on other unit.
  • Kindly tell me is there anymore troubleshooting is remaining to diagnose and resolve the issue or not.
  • Updated logs are also attached.

Please check the logs complete of let me know any further troubleshooting.

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. Check the control side of the contactor and see what the voltage is there. Is the contactor pulling in at all? I would request if you can call in when you are with the unit to your local tech support as they can walk through checking where we are losing the voltage to start the compressor.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:31 AM

Dear Team,

Voltage has been checked by manually volt meter which was 230VAC. But magnetic contactor was not pulling in, even controller board is not sending signal to contactor to pull in.

Regards

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. If we have 230V at the control side of the contactor (on a and b) and it is still not pulling in, then we have a bad contactor which will need to be replaced.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:09 PM . Last Modified: ‎2024-02-14 02:22 AM

Hello, I think generally mother board sent the command to magnetic contactor to pull in. But  at this issue no commands comes from mother board thats why compressor unable to start. Am i right????

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. The motherboard sends a signal to relay 400 to pull in the contactor. Per the picture below, if we are getting 230 volts across 70-4 and 70-6 then the relay is getting pulled in and the contactor is bad. If we are not getting the 230V at these points then we will have to go backwards and find out where we are losing the control voltage to the contactor. See the attachment below.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

Dear team,

Please tell me, can we exchange or replace the mother boards or ACRP102 to ACRP501 or ACRC 103 to ACRD101? Is unit can be operational by this replacement or not???

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-01-29 11:37 PM

0 Likes
0
4709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-01-29 11:37 PM

Hello. The motherboards are the same on all the Inrow units, however the cards and jumpers that are plugged into the motherboards are different on some of the units. You will need to make sure to keep all the cards and jumpers with the proper unit when swapping the motherboards.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
4710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:10 PM . Last Modified: ‎2024-02-14 02:31 AM

Thanks for your usual support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of