APC9630 installation in SMT2200

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC9630 installation in SMT2200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
11
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

APC9630 installation in SMT2200

The plastic liner of the SmartSlot enclosure of the SMT2200 has 2 tabs that protrude from the case. The slot cover has 2 slots, through which the tabs pass, to allow the cover to fit flush against the case.

The APC9630 has 2 slots as well, but the slot at the left end does not align with the tab at the left end of the SmartSlot. This prevents the APC9630 from sliding into the SmartSlot.

I found nothing in the documentation for either the SMT2200 nor the APC9630 that mentions the tabs. Do the tabs exist for a reason? Does the fact that the left tab and slot don't line up indicate that the APC9630 cannot be used in the SMT2200, even though the APC web site lists the APC9630 as an accessory for it?

Thanks in advance for any assistance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • network_management_card
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:32 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:32 AM

The plastic liner of the SmartSlot enclosure of the SMT2200 has 2 tabs that protrude from the case. The slot cover has 2 slots, through which the tabs pass, to allow the cover to fit flush against the case.

The APC9630 has 2 slots as well, but the slot at the left end does not align with the tab at the left end of the SmartSlot. This prevents the APC9630 from sliding into the SmartSlot.

I found nothing in the documentation for either the SMT2200 nor the APC9630 that mentions the tabs. Do the tabs exist for a reason? Does the fact that the left tab and slot don't line up indicate that the APC9630 cannot be used in the SMT2200, even though the APC web site lists the APC9630 as an accessory for it?

Thanks in advance for any assistance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

yes, you can contact APC support for one with the serial number of your AP9630/31 and we can send it out for you immediately.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

yes it works fine, we just need to send you a new updated faceplate. the earlier NMC2 faceplates were not adjusted before the SMT's were released.

if you want to PM me your shipping address/account info, i'll send you out a new faceplate. please confirm its AP9630 (vs. AP9631) and I need a serial number from the card.

if you prefer, confirm your email address in your profile and I will contact you via that method instead.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

Thanks very much.

The part is AP9630. The s/n on the face of the card is BA0915012758, and the one on the reverse is 1026819900041936.

The email in my profile is accurate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

I've got a similar problem with a Smart-UPS X 1500VA Rack/Tower LCD 230V SMX1500RMI2U and a Network Management Card 2 AP9630 we had delivered last week.

Is it again an old style faceplate issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

The first four from the UPS are AS1037. The NMC2 are BA0909.

I'll PM you in a mo.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

most likely, if the tabs dont line up. are the "slots" on the NMC faceplate the same side on the front of the NMC? also, you can provide the first four characters of your serial number, such as JA0925, and i can most likely confirm if its the answer or not.

if that is the case, i'd recommend contacting tech support for a replacement faceplate. i am in the USA but i see you are in the UK, else I could ship you one. i can still do so if you want though? PM me your address if you want.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

I'm in the same vote, I have an AP9631 Card that won't fit due to the tabs not lining up, I can't seem to find a location online to buy the updated faceplate. Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

Info

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

hi graham,

AP9619 is not compatible with SMT2200 even if you change the faceplates on them. You need get AP9630 or AP9631 which should hopefully ship with the correct faceplate already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:33 AM

Thanks for the information

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:32 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:44 AM . Last Modified: ‎2024-03-14 12:32 AM

The plastic liner of the SmartSlot enclosure of the SMT2200 has 2 tabs that protrude from the case. The slot cover has 2 slots, through which the tabs pass, to allow the cover to fit flush against the case.

The APC9630 has 2 slots as well, but the slot at the left end does not align with the tab at the left end of the SmartSlot. This prevents the APC9630 from sliding into the SmartSlot.

I found nothing in the documentation for either the SMT2200 nor the APC9630 that mentions the tabs. Do the tabs exist for a reason? Does the fact that the left tab and slot don't line up indicate that the APC9630 cannot be used in the SMT2200, even though the APC web site lists the APC9630 as an accessory for it?

Thanks in advance for any assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore