APC UPS 5000 Output Power Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS 5000 Output Power Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
14
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

APC UPS 5000 Output Power Error

Hi,

I just received in a new APC UPS SURTD5000XL rack mount system and have just finished setting it up. I have everything running fine and my servers are connected to the system and are working fine as well.

When I login to the UPS thru the Network Management Card Web interface, I see the following error:

1 Critical Alarm Present
- Output Power turned off

What does this mean? Everything is powered up correctly and the web interface shows the UPS is getting the power and such, but this error remains?

Can anyone help with this as to what may be causing the issue?

Thanks a lot.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • battery
  • hardware
  • network_management_card
  • NMC
  • output
  • power
  • smartups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

Can anyone help with this error?

Thanks in advance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Reseating the management card fixed the problem!!

Thanks alot "winna" for all the help you gave, it was most appreciated and very helpful!!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

Can anyone help with this error?

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-14 12:34 AM

no problem 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

Here you go, although it doesn't look like it says anything. The GUI still shows the error though.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

hi

you probably want to check the Logs tab in the network management card to get the full story of whats happening. we'd want to look at the event log first and maybe look at the data log.

you can also post the logs for us here to take a look at. you can follow [these instructions|http://nam-en.apc.com/app/answers/detail/a_id/9321/] to do so.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

thanks! i recently updated that article and made a mistake, i apologize. we also need event.txt, which is the most important. thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:34 AM

i agree. the subject line of your thread says output power error? can you show a screenshot of that or where did you see it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

sorry, i forgot to check back yesterday.

do you have devices connected to the UPS? this error is telling us that the network management card things the output power is off.

what happens if you click on Control on the left hand side from that screenshot. does it say turn UPS output on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Hi,

Yes, there are devices connected to the UPS. When I click on control on the left side, it does not say turn the power on. It gives me the following options:

Reboot UPS
Turn UPS Off
Put UPS to Sleep
Put UPS in Bypass
Signal PowerChute® Server Shutdown

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

see if you can do a screenshot, your copy and paste didnt display for me. thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Screenshot attached.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Hi,

I just noticed something else to. If I go into UPS->Status, if I look at the first line, I see the following error. Screen shot attached as well.

Last Battery Transfer: Unacceptable utility voltage rate of change.

Could this have something to do with it?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

hmm no, i don't think so. everything looks fine except for that alarm that is stuck there. can you try the following -> go to the Administration Tab->General->Reset/Reboot->Reboot management interface. Let's try and reboot the management interface to see if this problem clears. This will not affect load status in anyway.

if this doesnt work, are you or anyone else local to the unit? we could try reseating the card to clear the alarm and go from there.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Reseating the management card fixed the problem!!

Thanks alot "winna" for all the help you gave, it was most appreciated and very helpful!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

0 Likes
0
4556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-14 12:33 AM

Hi,

I just received in a new APC UPS SURTD5000XL rack mount system and have just finished setting it up. I have everything running fine and my servers are connected to the system and are working fine as well.

When I login to the UPS thru the Network Management Card Web interface, I see the following error:

1 Critical Alarm Present
- Output Power turned off

What does this mean? Everything is powered up correctly and the web interface shows the UPS is getting the power and such, but this error remains?

Can anyone help with this as to what may be causing the issue?

Thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore