APC9630 NMC false positive issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC9630 NMC false positive issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:54 AM

0 Likes
15
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:54 AM

APC9630 NMC false positive issue

A few Apc9630 NMC in our organisation indicate a false positive "on battery" via snmp only after a battery test. It's always the same NMC and facilities with multiple cards only 1 will have the issue.

We have updated the FW to the latest. Has anyone seen this issue?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Hello Eric,

since me and my colleague are experiencing exactly the same error with 2 of our AP9630 installations, I'm curious if you have found a solution to this problem? I'm sorry for replying to this relatively old thread - but as of now the APC technical support of Germany wasn't able to help me.

Thanks in advance and best regards
Mikis

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Hi Eric,

Is it possible for you to send us a copy of your NMC's log files as well as the screenshot of the SNMP that you were getting? Kindly follow the steps outlined on the kbase listed below on how to download the log files.

[How can I download Event logs and Data logs and Config.ini from the Network Management Card?|http://nam-en.apc.com/app/answers/detail/a_id/9321/kw/downloading%20event%20logs]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Sorry for the long reply, I only remember about this when it happens.

I attached all the files in the event after we see this:
"11/17/2011 19:15:41 UPS: Started a self-test. 0x0137"
Is when the NMC returns a false positive from this OID:
.1.3.6.1.4.1.318.1.1.1.4.1.1.0

Thanks in advance!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Sorry I completely missed the second part.

Yes we are walking the OID, we can't use traps for some reasons I can't go
into. It gets polled every 5 min, and we would understand if the status was "3" only during the test that would explain the problem but this OID polls as "3" forever after a battery test is finished or until we reset the NMC.

In the picture that was 1 hour after the battery test in the log.

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

can i ask what model of UPS this is in just incase we need that?

also, that is the OID for UPS basic status. how often are you polling that OID? cause to me, its not a trap your getting but a GET on an OID for status. when the UPS does a self test, it is on battery, which is what the 3 indicates in the response. 2 indicates online. if you are polling this often and every single time the UPS does a self test, technically its not incorrect and we may need to just adjust your configuration and how its looking at that OID. i thought it was a trap you were getting but i dont think so.

.1.3.6.1.4.1.318.1.1.1.4.1.1
.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsOutput.upsBasicOutput.upsBasicOutputStatus

The current state of the UPS. If the UPS is unable to determine the state of the UPS this variable is set to unknown(1).

onLine (2)
onBattery (3)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Both of these units are identical all the way down to the manu dates:

Model: Smart-UPS 3000 ( SMT3000RM2 )
Serial Number: ------------
Firmware Revision: UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0 (ID18)
Manufacture Date: 02/04/2011

Apparent Power Rating: 3000 VA
Real Power Rating: 2700 W

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

alrighty good to know. any other comments on what i said as far as how you guys use that basic output status OID?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

ok, i will start to look into this. i noticed in your log that the NMC is not logging a self test passed event so i am wondering if the NMC is not seeing the correct status when the self test is complete and thus is not logging the self test passed event which is also affecting the output OID.

give me a few days to replicate and investigate and I will see what we find. i might not be able to post back until early next week since i'll be on vacation but i will make a note here. i need to track down some similar units to see if i can replicate.

Edit - i was able to do this quicker than i thought. i have a similar unit and i tried it on the same NMC firmware (AOS 5.1.6/sumx 5.1.6) by commanding a self test and did not see the issue. the OID changed back to online after my self test completed. are you able to replicate the issue this way as well or only when the UPS does its scheduled self test?

depending on what you say, the only difference I see is the firmware on my unit is newer and if we are stuck, i might suggest we try to upgrade one of yours.

my unit had UPS 08.0 / MCU 12.0 / UBL 08.4 / MBL 12.0 (ID18). i also tried on a few other models and did not replicate the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Hi,

I have several Smart-UPS 3000 with the same issue. I poll all my UPS units daily and several of these models constantly show On-Battery. I'm checking about 1500 UPS units and it's just a handful that have this problem.

I'm checking against: 1.3.6.1.4.1.318.1.1.1.4.1.1.0

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Hey guys,

I want to reiterate that we have upgraded to the latest FW on the APC site and the cards affected are in sites that have multiple units that were all purchased at the same time.

One card will have this problem consistently where the other does not.

PS.
I'm glad Mike posted to show that we are not crazy. ๐Ÿ™‚

EDIT:

here is the info on my firmware

Hardware Factory

Model Number: AP9630
Serial Number: JA1117020435
Hardware Revision: 05
Manufacture Date: 04/24/2011
MAC Address: 00 C0 B7 58 D4 02
Management Uptime: 5 Days 14 Hours 36 Minutes

Application Module
Name: sumx
Version: v5.1.6
Date: Aug 11 2011
Time: 10:01:53

APC OS (AOS)
Name: aos
Version: v5.1.6
Date: May 11 2011
Time: 11:35:16

APC Boot Monitor
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57

Message was edited by: Cladmonitor

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

I believe that the firmware i picKed a winna is referring to is the UPS's internal firmware, which is separate from the management card's firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

I realized that yesturday but after spending 30 minutes looking around I don't see
A) the firmware
B) Any way to upload it/apply it.

Any guidance on thoes would be helpful.

Thanks,
Eric

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Thanks guys Ill do that and let you know of our findings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:24 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Terry was right, i_picked_a_winna posted the firmware of her UPS (UPS/MCU/UBL). On newer Smart-UPS (SMT and SMX) the firmwares can be upgraded. You will need to call our Technical Support Hotline in order to obtain the correct files for your UPS and it needs to be done over the phone. Failure to follow a step can lead to UPS being bricked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

You'll need to wait for one of the APC folks to respond. In the older APC products that I have, the firmware is in one-time-programmable parts. I believe that in at least some of the newer APC products, there is some way to field update it. I suspect that it isn't in the general download area because unlike the management card which isn't critical to basic operation of the UPS, it is critical to the operation of the UPS and a problem in the update process could render the UPS unusable to the point where you'd have to ship the whole UPS back to APC for repair.

Message was edited by: Terry Kennedy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 03:25 AM . Last Modified: โ€Ž2024-03-13 02:53 AM

Hello Eric,

since me and my colleague are experiencing exactly the same error with 2 of our AP9630 installations, I'm curious if you have found a solution to this problem? I'm sorry for replying to this relatively old thread - but as of now the APC technical support of Germany wasn't able to help me.

Thanks in advance and best regards
Mikis

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of