APC UPS with "DC output"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS with "DC output"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
7
4312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

APC UPS with "DC output"

Hello,

 

I am looking for a DC-output APC UPS, I found these:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=CP27U13SC3&tab=models

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=CP27U13NA3-S&tab=models

 

But its only 27 Watt with one 7A battery, I need 100 Watt with 2 or 4 batteries.

 

Please suggest, if there is anyone?

 

Thanks

Shakeel

Pakistan

Labels
  • Labels:
  • General Questions & Suggestions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Shakeel,

Here is what I can provide.

1.) I can only see charging wattage. You could maybe figure out the charging amperage from this. SUA750I - 50W, SUA1500I - 136W

2.) These SKUs are not designed to support external battery packs. Only SKUs that have "XL" in the part number for SUA models support external battery packs. If you have an SUA750XLI, for example, the battery packs are not automatically detected and the UPS must be told they are attached for the reason of reporting proper runtime.

3.) No, these units are designed for use with lead-acid batteries only.

4.) I am not sure on this since the UPS is not designed to be used with this size of a battery. The chargers are very tiny based on the standard battery included so I estimate it'd take a long time..

5.) No, not that we'd recommend or support. I don't know if they exist out there in the world but I am sure they do. If you're familiar with this type of thing, you could use an external charger to charge these batteries and then somehow connect them to the DC bus of the UPS.

6.) We technically don't support this. If you want to move forward at your own risk, you'd want to look into an external charger for sure.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Those were the "Powershield" devices that I don't think we make anymore and they were for Telco applications. We only offer DC rectifiers today I believe under the "Magnum VS" line. Some of those are listed here http://www.apc.com/products/family/index.cfm?id=470 along with the one "Powershield" unit I still see listed, though I do not believe we actively sell Powershield (at least in the US where I am). 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Hi Angela

Thanks for your reply

 

I want to operate my laptop on a DC UPS i.e. by bypassing laptop's charger and directly connecting it to 12V DC UPS. My laptop is Sony VAIO Core i5. Do you think it would be possible and its a safe method?

Why I am doing so? Here, in Pakistan, there are very long sessions of load-shedding and power failures, and power is not available for enough time even to fully charge a 100 amp battery.

On a 100 amp battery, if a 70watt laptop lasts for 3-4 hours, it might lasts for 8-10 hours if operated on DC (19.5V), because there are a lot of power losses in DC to AC conversions.

 

Please suggest any solution.


Thanks
Shakeel
Pakistan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Hi Shakeel,

I am not sure about what you want to do and how you specifically would do it but I don't have any experience with this type of application and doing this type of thing. I really can only provide input personally on our AC power solutions. I can understand the dilemma you have though and why you want to do it and ir anyone else wants to post and contribute, please do.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

There are stand-alone battery chargers for some Sony VAIO models. For example:

http://www.brilliantstore.com/laptop_battery_chargers_portatechs_elc_1095.html

I have no idea if it's any good. Due to limits of the battery chemistry, I'm not sure you'll be able to charge the batteries faster, but you can charge multiple batteries at the same time and swap them while working.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Thanks voidstar for your suggestion

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Hi Angela

I am using two APC, one is SUA750i for laptop and internet-device, and one is SUA1500i for all other appliances. But the charging rate of both is very slow i.e. slow for our requirements with heavy load-shedding, where utility power is available for a limited time. We face 10-15 hours of load-shedding in summer. So, we have a limited time to charge batteries.

  1. What is the charging current of SUA750i and SUA1500i? Can it be increased? Does it varies according to the load applied to UPS?
  2. How many maximum "Battery Packs" can be attached to SUA750i and SUA1500i? If extended battery packs are attached, would these be automatically recognized by APC? 
  3. Does APC support any 24V dry battery of 100 amp/200 amp?
  4. Could you please explain how much time SUA1500i takes to fully charge a 100 amp battery?
  5. Is there any external charger to boost charging and that is also compatible with APC?
  6. Please suggest how APC (SUA750i /SUA1500i or any other model) can be used to quickly charge a 200 amp (or 100 amp) battery in just few hours?

Thanks

Shakeel

Pakistan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

0 Likes
0
4309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:18 AM . Last Modified: ‎2024-03-19 03:00 AM

Shakeel,

Here is what I can provide.

1.) I can only see charging wattage. You could maybe figure out the charging amperage from this. SUA750I - 50W, SUA1500I - 136W

2.) These SKUs are not designed to support external battery packs. Only SKUs that have "XL" in the part number for SUA models support external battery packs. If you have an SUA750XLI, for example, the battery packs are not automatically detected and the UPS must be told they are attached for the reason of reporting proper runtime.

3.) No, these units are designed for use with lead-acid batteries only.

4.) I am not sure on this since the UPS is not designed to be used with this size of a battery. The chargers are very tiny based on the standard battery included so I estimate it'd take a long time..

5.) No, not that we'd recommend or support. I don't know if they exist out there in the world but I am sure they do. If you're familiar with this type of thing, you could use an external charger to charge these batteries and then somehow connect them to the DC bus of the UPS.

6.) We technically don't support this. If you want to move forward at your own risk, you'd want to look into an external charger for sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore