Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Please select a country to continue with beta search.
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM

Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM
Hi Hazan,
The red LED indicates your UPS is reporting a fault. According to the series of lights lit up above the battery bar graph on the right hand side, this UPS is reporting an inverter fault, meaning something has malfunctioned with the internal component in the UPS that converts the DC battery power generated by the battery to AC power that is output by the UPS.
The recommended next step is to perform a brain dead of the UPS, which I will outline below:
1. Turn off the UPS.
2. Unplug it from the wall.
3. Unplug all load from the output receptacles.
4. Disconnect all batteries, including any extended run battery packs.
5. Wait 10-20 seconds and reverse the process to turn the UPS back on.
If this does not fix the issue, the UPS will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM
Hi Hazan,
The red LED indicates your UPS is reporting a fault. According to the series of lights lit up above the battery bar graph on the right hand side, this UPS is reporting an inverter fault, meaning something has malfunctioned with the internal component in the UPS that converts the DC battery power generated by the battery to AC power that is output by the UPS.
The recommended next step is to perform a brain dead of the UPS, which I will outline below:
1. Turn off the UPS.
2. Unplug it from the wall.
3. Unplug all load from the output receptacles.
4. Disconnect all batteries, including any extended run battery packs.
5. Wait 10-20 seconds and reverse the process to turn the UPS back on.
If this does not fix the issue, the UPS will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-25 07:34 PM
Hello my name is Daniel, i have the exact same problem with my APC, i followed the steps you included below as a posible solution, but it didn´t work, i completely disarmed the UPS, you mentioned that it is a problem with the UPS inverter but im having trouble finding this inverter there are no diagrams available and im just recently beginning my work with this devices any help or advice could really help me...