Hello sir
I have a Apc ups model SRC 2000
which is showing eerror
inf III
Error image is attached also for your reference.
Please advise me how to fix this error
Wait for quick reply
Email: kamran.jeddah@yahoo.com
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:05 AM . Last Modified: 2024-03-19 02:35 AM
Hi Mohammad
That would be an inverter fault. You maybe able to clear it by 'Braindeading' the UPS. Disconnect the AC power to the UPS and the Battery power for about 10 secs and then reconnect it.
If that doesn't work the UPS would need to be replaced.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:05 AM . Last Modified: 2024-03-19 02:35 AM
Hi Mohammad
That would be an inverter fault. You maybe able to clear it by 'Braindeading' the UPS. Disconnect the AC power to the UPS and the Battery power for about 10 secs and then reconnect it.
If that doesn't work the UPS would need to be replaced.