We have an APC Symmetra LX 8 KVA with an expansion battery module and 3 PDU panels on the back of the device. I have 5 PDU's plugged into the 20A circuits. The load is currently showing about 75%. However, when I go into the statistics of that load, it shows phase 1 has 39% load and phase 2 has 75% load. My question is how do I adjust this to better balance the load between the 2 phases? Is there a standard on which PDU panels are used on which phase?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:26 PM
Nope, that's it! That answers my question and I'll get the load adjusted. Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:26 PM
Assuming you have a rackmount/tower unit and are using the "default" backplates (two 5-20 outlets and an L14-30) as seen below:
http://www.apc.com/products/moreimages.cfm?partnum=SYA8K16RMP&type=Back
The "top-left-most" 20a outlet of the three (per backplate panel) will exclusively draw off of phase 1. The "right-most" 20a outlet will exclusively draw off of phase 2.
If you have purchased a different type of backplate, let us know the model # so we can assist further.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:26 PM
Nope, that's it! That answers my question and I'll get the load adjusted. Thank you