Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
APC Symmetra 40k Power Module, Battery Module, Intelligence Module.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2602:47 AM. Last Modified: 2024-03-1901:51 AM
Hi,
Whenever any module or card is to be reseated or replaced the UPS should be placed into Maintenance Bypass before proceeding. This will eliminate any possibility of system downtime. This procedure applies to: Intelligence Modules, Power Modules, Static Switch Modules, Battery Monitor Boards, Power Supplies, XR Communication Cards and External Switch Gear Cards.
Please follow the Installation and Operation Guide for instructions on how to place a Symmetra PX into bypass. And you should verify compatibility of any replacement modules with local support before proceeding.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2602:47 AM. Last Modified: 2024-03-1901:51 AM
Hi,
Whenever any module or card is to be reseated or replaced the UPS should be placed into Maintenance Bypass before proceeding. This will eliminate any possibility of system downtime. This procedure applies to: Intelligence Modules, Power Modules, Static Switch Modules, Battery Monitor Boards, Power Supplies, XR Communication Cards and External Switch Gear Cards.
Please follow the Installation and Operation Guide for instructions on how to place a Symmetra PX into bypass. And you should verify compatibility of any replacement modules with local support before proceeding.