APC SmartUPS 3000XL not working on Generator Power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SmartUPS 3000XL not working on Generator Power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
5
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

APC SmartUPS 3000XL not working on Generator Power

All,

I know this subject has probably been beat to death. (i've searched and read).

I'm at witts end. It is a state requirement that we be able to operate on alternate power for up to one week.

We have Generators
We have the electrical wiring
We have ELECTRICITY to all of our equipment BUT what's connected throught the UPS's

I have adjusted the Voltage sensativity to LOW and they still wont accept power from the generator.


We're on a budget (meaning the company is stingey)

Is there some kind of device that we can put 'in line' with the power coming from the generator to 'regulate' the power so that the UPS's will accept the power??

If not - what do you suggest (buying new generator or new UPS is not an option)

I can only think that we bypass the UPS.............


Seriously - we dont have much equipment (two servers, a dialer and a router + hubs and such). During Hurricane Isabel I ran electrical equipment at my house for TEN DAYS with a portable generator and the gear lived........

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000xl
  • generator
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

Hi There

I just wondered how you got on as I too have the same problem. We have installed a 2 cylinder diesel generator and although everything runs fine apart from a very slight flicker of the lights, the Smart UPS 1500 refuses to go back on to mains power.

What test equipment can I use to check the frequency please? I am in the UK so am operating on 240v. Is there any way I can find out from the APC UPS why it does not want to go on to mains power?

Thanks

John

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

i assume there is no adjustment of any sorts on this generator? are you able to verify what the issue actually is (with a voltmeter or oscilloscope)? is it voltage out of range? frequency out of range? rate of change? do you have any software/management accessories installed to check the data and event logs to see what the issue is reported as?

it may be a good idea to try and figure out what variable is causing the UPS to go to battery so we can find the correct solution, because it may require something different depending on what it is (voltage, frequency, etc)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

Wow - a LOT of great questions there........

Have to do some verification then re-schedule a test of the generator and take the necessary measurements.


Do I take the Frequency and Voltage meaasurements while the load form the UPS's is applied - or while the load is NOT applied? (which - or both?)



THANKS!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

i would take the measurements from a receptacle that is providing output power from the generator - so maybe the outlet that the UPS is plugged into? remove it temporarily and check to see what it is inputting to the UPS.

that'd be the best spot in my opinion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

Have scheduled power generator test scheduled for this coming Friday (11/12) We'll see what happens - and will post results here!

Message was edited by: johnnyz1234

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:11 AM . Last Modified: ‎2024-03-13 11:25 PM

Hi There

I just wondered how you got on as I too have the same problem. We have installed a 2 cylinder diesel generator and although everything runs fine apart from a very slight flicker of the lights, the Smart UPS 1500 refuses to go back on to mains power.

What test equipment can I use to check the frequency please? I am in the UK so am operating on 240v. Is there any way I can find out from the APC UPS why it does not want to go on to mains power?

Thanks

John

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of