APC Smart-UPS U.S. to Japan

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS U.S. to Japan
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
CShock
Crewman CShock
Crewman

Posted: ‎2024-04-03 09:34 PM

0 Likes
8
2085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-03 09:34 PM

APC Smart-UPS U.S. to Japan

What if any problems would there be with using a Smart-UPS 1500 configured for the U.S. (120V) in Japan (100V)? For what it's worth, every U.S. product charges/works with the 100V. Thinking of taking the UPS with me the next time I return to Japan.

 

Thank you for your time.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-04 04:53 AM

0 Likes
3
2070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-04 04:53 AM

Really depends on which model UPS you have and how it’s designed. If the unit is a multi voltage / multi frequency unit it may operate fine.

 

Depending upon where you’re in Japan the frequency can be either 50 / 60 Hz. The line voltage is 100 VAC throughout Japan.

 

If your unit allows you to adjust the power quality and the transfer voltage - do so. Otherwise the unit will constantly be running on battery only power and thus reduce the service life of the same.

 

Meaning the unit will never go on line (AC Mains) and will drain the internal batteries.

 

You’ll need a universal adapter in case the site you’re at only has the two prong outlet vs three prong. Which leads to the last problem of a building wiring fault error.

 

If your location doesn’t have a three prong grounded outlet. The unit will constantly declare a building wiring fault. Because it doesn’t see a proper grounding system in place.

 

Good luck, let us know what you decide to do. If the information proves helpful please do mark this question as solved. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

CShock
Crewman CShock
Crewman

Posted: ‎2024-04-04 03:51 PM

In response to Teken
0 Likes
1
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-04 03:51 PM

Thank you Teken.

Now all I need to do is find someone who sells APCs in Japan. Attempts to reach D & H Distributing Company, Ingram Micro, and TD SYNNEX Corporation have not gone well. No voicemail or method to speak to a live person.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-09 07:48 AM

In response to CShock
0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-09 07:48 AM

If the information provided was on topic and resolved the question please insure you mark this as solved. So the information can assist the next person asking the same. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

CShock
Crewman CShock
Crewman

Posted: ‎2024-04-09 05:00 PM

In response to Teken
0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-09 05:00 PM

My apologies for the delayed response. The models I have indicate the following:

Nominal Input Voltage: 120 VAC

Input Voltage Range: 82 t0 144 VAC

Input Voltage Adjustable Range: 75 to 154 VAC

Input Frequency: 50/60 Hz +/- 3 Hz

Nominal Output Voltage: 120 VAC

 

Based on this, it appears to indicate (1) with a 100V input, the APC will provide 120V output or (2) with a 100V input, the APC will provide a 100V output.

I found a forum of other peeps using APC units (towers) in Japan and they reported the systems run without issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

CShock
Crewman CShock
Crewman

Posted: ‎2024-06-20 04:41 PM

0 Likes
2
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-20 04:41 PM

Update: The APC works perfectly. I'm guessing since the (Japan) input voltage is 100V, and falls within the required APC specs, the output from the APC plugs are 100V.

 

You can plug a US model APC into a Japanese outlet. Please note the residence where the APC unit is located, has three-pronged outlets (ground). Questions or comments...send them my way.

 

Thank you Community.

Reply

Link copied. Please paste this link to share this article on your social media post.

CShock
Crewman CShock
Crewman

Posted: ‎2024-06-21 12:39 PM

In response to CShock
0 Likes
1
1877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-21 12:39 PM

Another update. I may have spoken too early. It appears the APC goes to the battery when under a full load. For small items such as phone chargers the APC ran without any problems. However, when I plugged in a desktop computer and monitors, the batter immediately kicked in. The battery drains, but at a much slower rate since it continues to receive a 100V charge. I'll continue testing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-06-24 04:00 AM

In response to CShock
0 Likes
0
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 04:00 AM

Adjust the upper and lower transfer voltage and report back how the system operates. Based on your last reply the system is running on battery only power which isn’t ideal or fine.

 

Ideally the system would be running on AVR mode to trim / boost the input line voltage. Given the system is still plugged into AC Mains and the battery continues to drain indicates the unit is on battery only and not AVR.

 

This assumes the unit you have has AVR circuitry. 

Reply

Link copied. Please paste this link to share this article on your social media post.

CShock
Crewman CShock
Crewman

Posted: ‎2024-06-24 05:48 AM

0 Likes
0
1873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 05:48 AM

And yet another update. While using the APC unit, the display said the battery needed to be replaced. I ran a test and the unit said the system passed. Luckily, I had another APC. I set it up and it's been running for that past 2 days without the use of the battery. It is currently under a 17% load (running a Mac Pro (desktop), XDR and external SSDs). I've seen the load slightly exceed 20% based video tasks. Tomorrow, I'll plug in the other monitor and then one of the NAS boxes. I'll also be ordering a new battery for the 1st APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore