AP9640 3.1.1.1 Upgrade Issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9640 3.1.1.1 Upgrade Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
TechJen
Crewman TechJen
Crewman

Posted: ‎2024-06-21 07:37 AM . Last Modified: ‎2024-06-21 07:46 AM

0 Likes
1
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-21 07:37 AM . Last Modified: ‎2024-06-21 07:46 AM

AP9640 3.1.1.1 Upgrade Issues

Hello tech friends, I have a conundrum I'm dealing with here and hoped someone here might have more insight to prevent these issues.

 

I manage a fleet of 3500+ UPS's with AP9630 and AP9640 webcards, installed all over the US and CAN. We manage this fleet through DCE. We do not have highly technical people on-site to plug into these using the console port, we rely on them to do simple resets and troubleshooting when needed.

 

Previously we used to upgrade the firmware using the WinSCP File Transfer program, as I had negative experiences using the Schneider Utility to upgrade the firmware, it would not resume upgrades after network interruptions, resulting in a "bricked" webcard that needed to be reset to defaults with a user on-site or replaced. Because of this we avoided using the Schneider Utility, and just used WinSCP which resumes transfers, and had a very low rate of failure when upgrading NIC firmware. 

 

We have begun to use DCE to upgrade our fleet, as doing 1400 devices one-by-one using WinSCP was not practical. Up until now, doing upgrades through DCE has allowed file resuming and has not bricked many cards.

 

Recently, we have been trying to get all the NIC firmware up to date. I went through and upgraded all SY and SUMX AP9630 and AP9631 firmware to 7.1.2 with a fair amount of success, there were 1-2 failures which required a webcard replacement or reset. 

 

I then went through and upgraded our SY firmware from 2.3.1.1 to 3.1.1.1 without incident. 

 

I am now attempting to upgrade SU 1.3.3.1 and 2.3.1.1 to 3.1.1.1 and did a test run of 71 devices. Of those 71, 12 did not take the update and "bricked" in the sense that the IP no longer pinged. Having an end-user reboot and re-seat the webcard did not fix the issue. We found the only solution was to have the user reset the webcard to defaults via the reset button, and then reprogram the IP Subnet and Gateway. This of course wipes all our configurations, however it did take the upgrade and I was able to reconfigure from there using DCE.

 

Obviously I have concerns when doing the rest of the 1400 devices that I need to upgrade to 3.1.1.1. I am approaching this by using WinSCP to upgrade 1.3.3.1 firmware to 2.3.1.1 firmware, then from there will jump to 3.1.1.1, however I would like to avoid a high number of these resets, since it requires our support team to work on these with end-users, which can take days or weeks to complete, all the while the NIC is offline during this situation.

 

Does anyone have any more advice to avoid these issues? Would a step-increase to specific versions be a better option, say 2.3.1.1 to 2.5.0.6 to 3.0.0.11 to 3.1.1.1 or something similar? I would like to avoid causing our Support team more headaches with these resets.

 

Thank you for the help in advance!

Attachments
  • Tags:
  • 1.3.3.1
  • 2.3.1.1
  • 3.1.1.1
  • ap9630
  • ap9640
  • dce
  • english
  • firmware
  • nic
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-06-24 06:50 AM

2 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 06:50 AM

A stepped upgrade is very time consuming but reduces the incident of a bricked NMC.

 

As it relates to upgrading over the WAN you’re simply playing with fire! ☝️

 

Anything to do with firmware upgrades on any APC hardware must be done locally or the very least via the LAN.

 

In 2024 APC / Schneider continue to use 1990 technology and has zero fail over protection relating to firmware protection / recovery! 👎

 

Almost every industrial device and security hardware we have incorporates a secure partition area. That allows the end user to recover / roll back to the previous firmware and working state.

All of these devices validate the firmware for compatibility, validity, and progress. 

If at any time the firmware should fail. The unit will simply stop, roll back to the previous firmware’s - good working state! 

In 2024 APC still doesn’t offer a high memory save, store, reload?!? Even if you were too cheap to incorporate this hardware you could do so in software!

 

As you noted in WinSCP . . . 

How can a piece of software written more than 15 years ago have the ability to RESUME, yet the actual maker (APC) not incorporate the same in their Wizard???

 

Answer = Lazy and incompetent! 🤦‍♂️👎

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore