Morning guys, I have this APC Smart UPS SUA2200 that doesn't start well
The only device connected is a 3Watt LED light
It is disconnected from main power.
As you can see in the video , after Power On, The fan is audible. But no output to the LED light.
I press the power button for a few seconds, the UPS comes to life for a brief second, the LED lamp lights up, then shuts itself down
If the Youtube didnt embed well, click this link [url]https://youtu.be/G1alNa2fdqI[/url]
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
Thnak you William, I ordered a voltmeter and will be able tp test this once I have it 🙂
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
If you have access to a DC volt meter, remove the batteries from the unit and check their voltage. As a pack, you should measure around 48 volts DC. Anything lower than that won't be enough for proper operation.
(It's possible for the battery voltage to measure normally under the very light load presented by a volt meter. I strongly suspect bad batteries are this unit's only problem, especially if they are more than five years old.)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:06 AM . Last Modified: 2024-03-18 02:46 AM
Thnak you William, I ordered a voltmeter and will be able tp test this once I have it 🙂