APC Smart UPS SUA1500i - new batteries, battery lights keep flashing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart UPS SUA1500i - new batteries, battery lights keep flashing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

0 Likes
3
4468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

APC Smart UPS SUA1500i - new batteries, battery lights keep flashing

I have an APC UPS SUA1500i about eight+ years old.

A few days ago I had to replace the old flat and dead batteries with new ones, and since then the battery lights on the unit keep flashing simultaneously. Batteries have been charging for more that 24 hours since changing. Have also set the date of newly installed batteries in Powerchute.

If power goes out, the UPS shuts down all connected equipment straight away. It seems that it reckons the batteries are drained.

Tried discharging the batteries and unplugged the UPS from the mains, discharging took about 30 minutes which indicates that the batteries are fully charged and working fine. Even after letting the unit fully recharge the batteries, the battery light indicators keep flashing.

Have tried calibrating with APC Power Chute Business Edition, but there is no difference.


Status in Power Chute is:

Device Status On Line, Battery Discharged (Software Update Available)
UPS Load 20.1%
Runtime Remaining 0 Minutes
Internal Temperature 23.4°C / 74.1°F
Load Power 20.10% VA
Load Current 9.1 Amps

- Power Status
Input Voltage 231.8 VAC
Output Voltage 231.8 VAC
Input Frequency 50.0 Hz
Output Frequency 50.0 Hz

- Battery Status
Battery Charge 53.0%
Battery Voltage 27.7 VDC

Battery Status
Battery Status Normal
Battery Charge 62.0%
Battery Voltage 27.7 VDC

Diagnostics
Self Test Status
Last Self Test Date 20 March 2020 07:57:39 CET
Last Self Test Status Refused

Runtime Calibration Status
Last Runtime Calibration Date 20 March 2020 07:57:48 CET
Last Runtime Calibration Status Passed

As you can see Last Self Test Status is Refused (every time I tried it, even after charging the batteries for more than 24 hours).

 

What can I do to make the flashing disappear and the UPS recognise the new batteries.

Thank you and wishing everyone all well.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • batteries
  • blinking
  • calibration
  • flashing
  • powerchute_business_edition
  • self-test
  • sua1500i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

0 Likes
0
4467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

Why keep things to myself only, I am always happy when a solution comes up and it helps others, too.

Cheers and #StaySafe

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

0 Likes
0
4467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

Issue solved.

Yesterday I did the weekly battery discharge process which took about 3 hours and 10 minutes. A sign that the new batteries are OK and working.

When batteries were completely flat I completely switched off the UPS with the power off button on the front panel, disconnected the mains, opened the chassis, took out the battery pack, disconnected the batteries, reconnected them after 10 or 15 seconds, closed the chassis, plugged the UPS to the mains and let the batteries charge without powering the UPS on.

And voila, this is it. Everything works fine, no more flashing battery LED lights.

  • Tags:
  • batteries
  • calibration
  • flashing
  • how-to
  • led
  • self-test
  • solution
  • sua1500i
Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

0 Likes
0
4467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

On 23/3/2020 3:38 PM, David said:

And voila, this is it. Everything works fine, no more flashing battery LED lights.

Nice work. Even nicer that you came back with an update. Always much appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

0 Likes
0
4468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:38 AM . Last Modified: ‎2024-03-07 10:53 PM

Why keep things to myself only, I am always happy when a solution comes up and it helps others, too.

Cheers and #StaySafe

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore