APC Smart UPS SMT2200RM2U Output Off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart UPS SMT2200RM2U Output Off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
7
60921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

APC Smart UPS SMT2200RM2U Output Off

We were getting a "replace battery" alarm from our rack mounted unit that was installed in 2011.  We purchased a new battery and installed it this weekend.  However, when we plug our items back in, no power is going to them.  I printed out the manual and found on the menu that the Output is Off.  I couldn't figure out how to turn the output to On.  Should it have worked immediately?  We currently don't have anything plugged into it since it wasn't transferring power to our computers.  The battery is now showing 98% power so I know that is working.

I don't know where the software is for the unit so all I have access to is the small display screen on the unit itself. 

Did we do something incorrectly when installing the new battery?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • output
  • smt2200rm2u
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
0
60879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

Hi Maggie,

The batteries are hot swappable meaning the UPS does not need to be turned off to replace it. It sounds like you're saying though you unplugged everything connected (your equipment), turned the UPS off, and replaced the battery but now the unit hasn't turned on? Or did something else happen? I am just wondering how the UPS output got turned off to verify how to turn it back on again.

If what I suspect is accurate, try these:

  • Hold down power button to see if it will prompt you to force an immediate ON to the outlet groups.
  • Verify your menu is in Advanced Mode (which can be selected by pressing Esc and then to Configuration menu by toggling it from Standard to Advanced). Once you do this, press Esc again and find the Control menu to command the outlets on using whichever option you need (with/without delay, etc).

Hope that helps get you started. The LCD can be a little misleading since when the unit is energized, the display comes on but not necessarily the Output power.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

Hi Maggie,

The batteries are hot swappable meaning the UPS does not need to be turned off to replace it. It sounds like you're saying though you unplugged everything connected (your equipment), turned the UPS off, and replaced the battery but now the unit hasn't turned on? Or did something else happen? I am just wondering how the UPS output got turned off to verify how to turn it back on again.

If what I suspect is accurate, try these:

  • Hold down power button to see if it will prompt you to force an immediate ON to the outlet groups.
  • Verify your menu is in Advanced Mode (which can be selected by pressing Esc and then to Configuration menu by toggling it from Standard to Advanced). Once you do this, press Esc again and find the Control menu to command the outlets on using whichever option you need (with/without delay, etc).

Hope that helps get you started. The LCD can be a little misleading since when the unit is energized, the display comes on but not necessarily the Output power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
0
60879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

my boss swapped out the battery this weekend. he said that our kind of unit needed to be opened up to get to the battery. and I looked at the unit and it does look like the battery is screwed in, and lot as easy to eject and swap out as the batteries on our server (which sound like what you described)

So yes, we powered down the unit, unplugged everything, installed the new battery, plugged it in and turned it on.  it recognized the battery and started charging it and we finally had an end to the endless beeping to change the battery.  But when we plugged in the servers to the apc, they weren't getting any power and looking at the menu, it said "Output off". 

So I just went back to the unit and tried your suggestions.  I held down the power button and after a moment I got a beep and a red light that says "fault state: output over volt".  but we don't have anything plugged in to the output.  so I don't know what is tripping the unit. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

Hmm, OK. Yeah, this unit needs to be opened to get the battery out but next time, you won't need to unplug all of your equipment or even turn the UPS off if it is not necessary for you. It would alarm at you while the batteries are disconnected and you'd have no battery back up during the time your swapping the battery but at a minimum, you shouldn't need to go through the hassle of unplugging everything, even if you'd prefer to turn off the load during the procedure in case of a power blip.

Moving on though, on the LCD, does it show you a good input voltage and battery voltage? I'd observe what those are reading. You could also check through the Logs menu and see if anything different than the fault you saw is listed there.

The next thing you can try is a braindead to reset the unit and see if anything changes. To do this:

  1. Turn off the equipment that is connected to the UPS. (Well, that's done already)
  2. Disconnect the UPS from its AC (input power) source.
  3. Turn off the output on the UPS either via the LCD or using the Power button (refer to your user's guide.) (That's already done too.)
  4. Remove the internal and external battery connections from the UPS for 20 seconds. (To do this, just unplug the connector for the battery - no need to unscrew it and slide the whole module out).
  5. It is now safe to remove or install a SmartSlot accessory card, reinstall the battery connections, and then plug the UPS back in and turn it on.

Then, try to force the UPS on one of those ways we discussed and see if the fault still exists. If it does, I'd suggest sending this thread and anything else you've tried to tech support (email or phone) to verify if there is anything else to try. 

Essentially, the UPS logic has detected an abnormal output voltage when it is trying to turn on which would not be good for the attached equipment so it is preventing the UPS from starting. I am not sure what would cause this unless you are aware of an event or incident before the replace battery popped up.

Let me know if you have any questions before you start. Or if you prefer, phone support can walk you through any of this step by step.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:42 PM

thank you for all your help Angela.  We never could get the unit to turn on the output and instead the unit stopped charging the battery, and the battery completely drained.  The unit is from 2011 and out of warranty.  We're just going to buy a new one and save us the headache of trying more to fix this one.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2025-12-10 12:28 AM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2025-12-10 12:28 AM

You're welcome Maggie - and sorry to hear! We do offer a Trade-UPS program if you weren't aware that you can do via a reseller/distributor or us directly. Even though the old unit may have a problem, you can trade it in to get credit towards a new one.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:50 AM . Last Modified: ‎2024-02-14 10:41 PM

Hello,

I had the same problem when i replaced my battery.  

after the replacement, i unplugged the power supply cable and i had the message: Fault state: Output Over Volt.

what can i do? i try a lot of options that i see from here and other topics and nothing.

 

tks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
60880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Hi Alain - 

Your issue is different in that it is displaying a fault. You can attempt to clear your fault by performing a "brain dead" procedure. To do this:

  • Turn off and remove connected load
  • Turn off UPS
  • Disconnect battery(s)
  • Unplug UPS from wall

You can now reconnect the battery and input power then turn the unit back on. If the fault clears you should be OK. If it persists you should contact your local APC Tech Support Team for further assistance.

 

thanks!

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore