AP9631 UPS Management Card does not complete self-test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 UPS Management Card does not complete self-test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

1 Like
2
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

AP9631 UPS Management Card does not complete self-test

APC | UPS Network Management Card 2

Hi,

One of our Smart-UPS 1500 UPS's  performs a self-test every 2 weeks, but never completes.
It flags as "down" in our monitoring software.

To correct this issue, we have to perform a reboot of the Management Interface.

We have set the Self-Test Schedule to "Never" and rebooted the management interface, but the self-test still runs as per the "Every 14th Day" schedule.

APC | UPS Network Management Card 2

Model: Smart-UPS 1500
SKU: SMT1500RMI2U

02.11.2015 14:48:32 UPS: Started a self-test.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9631
  • card
  • management
  • self
  • test
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Hi Omar,

Thanks for the log files. You're attempting to disable the self test in the right spot but why are you trying to disable it? Because it never finishes?

Are you strictly assuming the self test is occurring because of what is in the event log or has someone witnessed the actual UPS performing a self test?

I observed that both your UPS and AP9631 NMC firmware are out of date. I am wondering if this is some erroneous logging or the setting is not applying on the UPS. Regardless, I don't recommend you disable the self test and rather we find out why it does not say "passed." If you disable the self test, you may run into an issue with a failing battery which will be more of a headache in the end than letting the self test run in order to catch any failing batteries sooner than when it actually fails.

To upgrade the firmware on the AP9631, it is pretty easy and you can do it while everything is online with no affect on the NMC (besides a soft restart) and no affect to the UPS. I suggest we see if a firmware upgrade addresses this issue first. If it does not, I suggest we explore upgrading the UPS but for the SMT UPS upgrade, the UPS output must be turned off so this will likely require additional planning to do.

Here is information on upgrading the Network Management Card to 6.2.1 -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047

You can get the firmware from here (http://www.apc.com/tools/download/index.cfm) and Filter by Software/Firmware - UPS Network Management Cards and look for SFSUMX621. 

If we find that there is no change with the problem, upgrading the UPS itself is covered here: 

http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA170679

http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737 

I have a feeling these two issues are firmware issues somewhere but I am not sure where. The two issues are the NMC not reporting self test passed and the self test interval preference not applying.

Let me know if you have any questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Hello,

Just to be clear, the UPS is the component that does the self test - not the AP9631 Network Management Card. It is only reporting back to you what the UPS provides to it.

Can you provide the .tar file and attach it here from About->Support menu in the AP9631's web interface so we can review a few things including UPS firmware versions and event/data logs?

Instructions are here on providing the .tar file if you need it -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
0
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Hi Omar,

Thanks for the log files. You're attempting to disable the self test in the right spot but why are you trying to disable it? Because it never finishes?

Are you strictly assuming the self test is occurring because of what is in the event log or has someone witnessed the actual UPS performing a self test?

I observed that both your UPS and AP9631 NMC firmware are out of date. I am wondering if this is some erroneous logging or the setting is not applying on the UPS. Regardless, I don't recommend you disable the self test and rather we find out why it does not say "passed." If you disable the self test, you may run into an issue with a failing battery which will be more of a headache in the end than letting the self test run in order to catch any failing batteries sooner than when it actually fails.

To upgrade the firmware on the AP9631, it is pretty easy and you can do it while everything is online with no affect on the NMC (besides a soft restart) and no affect to the UPS. I suggest we see if a firmware upgrade addresses this issue first. If it does not, I suggest we explore upgrading the UPS but for the SMT UPS upgrade, the UPS output must be turned off so this will likely require additional planning to do.

Here is information on upgrading the Network Management Card to 6.2.1 -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047

You can get the firmware from here (http://www.apc.com/tools/download/index.cfm) and Filter by Software/Firmware - UPS Network Management Cards and look for SFSUMX621. 

If we find that there is no change with the problem, upgrading the UPS itself is covered here: 

http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA170679

http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737 

I have a feeling these two issues are firmware issues somewhere but I am not sure where. The two issues are the NMC not reporting self test passed and the self test interval preference not applying.

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore