Posted: 2023-01-11 02:48 AM
Hello,
We have around 900 Smart-UPS 750s in our estate across various shops and running PowerChute 9.1.1-604 on these.
We are configuring the install, then going to the website to check the UPS Load, and via the Data Log.
Some site we are seeing a constant load every 20 mins, ranging from 3.9% -> 5.9% which is what we would expect as we are running just 1 small load server of this.
Some sites, they are reporting 0.0% load all the time, we've physically checked these are they are setup as follows;
Power from UPS into Mains Socket
Cable from UPS into Single PSU Server
UPS/Serial Cable to Server.
Why would they be showing 0.0% all the time? The batteries show 100%, a self test passes and there is VAC, VDC and Hz values being pulled back.
Regards,
Posted: 2023-01-11 02:25 PM
Would you happen to have the model number of the UPS? Have you checked if all of them have the same firmware version?
Posted: 2023-01-12 04:29 AM
The model is Smart-UPS 750.
Firmware is showing as UPS 08.3 / MCU 14.0 (18-10) is there a way to update firmware if required from the web gui?
Posted: 2023-01-13 09:39 AM
For firmware upgrade information see Schneider Electric FAQ FA279197
https://www.apc.com/us/en/faqs/FA279197/
Have you checked to output status on the UPS via the LCD panel? What the LCD panel is displaying is what should be displayed in PowerChute.
Note: PowerChute version 9.1.1 is old. We are now shipping version 10.0.5.