Line input voltage reported incorrectly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Line input voltage reported incorrectly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
119
Erasmus_apc
Sisko Erasmus_apc
112
View All
Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Paradisebaker
Crewman Paradisebaker
Crewman

Posted: ‎2022-12-27 11:03 AM

0 Likes
2
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-27 11:03 AM

Line input voltage reported incorrectly

Hi All

I have a Smart UPS 1400 (model number SU1400RMXLIB3U) with a AP9617 network module in it.

I got this unit in 2008, have been replacing batteries as needed since, everything is fine.

But since some time, the unit ALWAYS goes into AVR, stating that the input voltage is at ~192-195 VAC, which is simply not true, I have measured it with 3 multimeters and the input is stable at 232VAC.

I have found some instructions in this forum on how to adjust this (Solved: Re: Help Pls!! UPS DL1400RM UPS No longer compensating for a high input voltage - Communitie...)but this seems to work only with a network module of the second generation like the AP9630.

Does anybody know how this can be done on a AP9617? I just cant get out of the configuration menue, maybe there is some hidden option for techs?

Thanks for all your help

BR

Markus

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-01 05:46 PM

0 Likes
1
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-01 05:46 PM

Hi @Paradisebaker 

 

The procedure that was given to the link that you have shared wouldn't matter if you have an AP9630/AP9617 since it communicates to the UPS directly and from what I see, that UPS has an AP9617.

 

As far as I remember, you would need the Smart Signaling cable (940-0024/940-1524) attached to the UPS and to a serial port on a computer and a terminal emulation software for the SU1400RMXLIB3U UPS.  Keep in mind as well that the APCUPSD is not from APC hence, it would be best to reach out through their e-mail lists.

Reply

Link copied. Please paste this link to share this article on your social media post.

Paradisebaker
Crewman Paradisebaker
Crewman

Posted: ‎2023-01-12 10:06 AM

In response to JonPro
2 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-12 10:06 AM

OK, finally got it working. It was basically as described in the other thread, I was just too ignorant to get it working.

In my case, the key was to remove the network management card from the UPS, as it would always intercept the serial signal (even though the serial port is attached to the UPS, not the NMC).

For documentation (probably for my own sake, as I will have forgotten all about it until the next time):

  1. Power off
  2. Disconnect / unplug network card
  3. Connect only special serial cable
  4. Power on
  5. Press Y (shift y)
    1. Output: SM
  6. Press 1 (one)
    1. No output
  7. After 4 seconds press 1 (one) again
    1. Output: PROG
  8. Press L (shift L)
    1. Output: current input voltage
  9. Press + or – (plus or minus) to adjust to actual voltage
    1. Output: registry value (i.e. B4, B5, B6…)
  10. Check voltage value with L (shift L)
  11. Repeat step 9 and 10 until value is correct
  12. Done

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of