APC Smart-UPS 48V or 192 V external Battery cables too short !!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS 48V or 192 V external Battery cables too short !!!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
4
2369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

APC Smart-UPS 48V or 192 V external Battery cables too short !!!

Do any of the APC folks who contribute to this forum know why APC's external battery packs have overly short cables ? IE, if you want to install the packs above the rack in the case of a Smart UPS XL or RT rack mount model you are out of luck - the cables are too short.

Later on, if you need to add capacity don't have space below the UPS for more packs you are forced to either relocate the UPS upwards or purchase expensive extender cables. OUCH !

Why can't APC would make a simple change and eliminate this headache...

Thanks , ....Dave

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
0
2367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

Battman wrote:
With all due respect KVar, I don't believe it is because of resistive losses...firstly, it is only a matter of adding a couple of extra inches of wire to the connecting cables that come out of the battery module and they would reach - taking into consideration there is already upwards of 2-plus feet of interconnection wiring between the jars, fuses, etc inside the battery modules. Secondly, if resistive losses were so critical to avoid then APC wouldn't be able to sell battery extension cables !

Dave
Perhaps it is to ensure the sale of high margin extension cable, which probably offers resellers with great overhead too.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
0
2367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

Good question Battman! While I'm certainly not someone that designed the units, I'm sure some of my comments were things that were taken into account.

Due to the pure weight of the UPS and battery packs, they are simply meant to be installed in the bottom of a rack. This certainly may mean that if you add packs for more runtime, then yes, you will need to move some equipment up in the rack. However, it seems that in most cases I've seen moving equipment is pretty common in an IT enviroment, unfortunately, ours just weighs more. The external packs are meant to be installed directly beneath the units, which seems pretty standard. Like you said, extensions can often be purchased if there are reasons otherwise.

A good reason for short cables is so there isn't a lot of excessive cable hanging around the bottom of the rack. We've all seen our fair share of cabling nightmares and birdsnests. Having short cables simply keeps the battery pack cables out of the way.

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
0
2367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

Battman wrote:
Do any of the APC folks who contribute to this forum know why APC's external battery packs have overly short cables ? IE, if you want to install the packs above the rack in the case of a Smart UPS XL or RT rack mount model you are out of luck - the cables are too short.

Later on, if you need to add capacity don't have space below the UPS for more packs you are forced to either relocate the UPS upwards or purchase expensive extender cables. OUCH !

Why can't APC would make a simple change and eliminate this headache...

Thanks , ....Dave
I^2R loss, especially with 48v.

Same amount of voltage is dropped per amp, regardless of system voltage, but at half the voltage you need twice the amp.
Twice the amp means twice the voltage drop. Twice the voltage drop at half the voltage means 4 times the percentage drop.

This is why.

Not sure why not with 192v.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
0
2365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

With all due respect KVar, I don't believe it is because of resistive losses...firstly, it is only a matter of adding a couple of extra inches of wire to the connecting cables that come out of the battery module and they would reach - taking into consideration there is already upwards of 2-plus feet of interconnection wiring between the jars, fuses, etc inside the battery modules. Secondly, if resistive losses were so critical to avoid then APC wouldn't be able to sell battery extension cables !

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

0 Likes
0
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:35 AM

Battman wrote:
With all due respect KVar, I don't believe it is because of resistive losses...firstly, it is only a matter of adding a couple of extra inches of wire to the connecting cables that come out of the battery module and they would reach - taking into consideration there is already upwards of 2-plus feet of interconnection wiring between the jars, fuses, etc inside the battery modules. Secondly, if resistive losses were so critical to avoid then APC wouldn't be able to sell battery extension cables !

Dave
Perhaps it is to ensure the sale of high margin extension cable, which probably offers resellers with great overhead too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore