APC Smart-UPS 3000VA (SUA3000RMI2U) wont power up

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS 3000VA (SUA3000RMI2U) wont power up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

0 Likes
6
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

APC Smart-UPS 3000VA (SUA3000RMI2U) wont power up

Hi there!

We bought an used Smart UPS 3000VA for our office. Until 3 weeks ago the USV was in proper use.

After move and built in, the USV wont start. There is no sound, no light, nothing. The power is correct connected, an tested. Is there inside an "power-protection" or something else?

Any ideas what we can do for test?

Thx an best regards.

Lukas

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

I have a DLA3000RMT2U that operates at 208 volt single phase (should be same topology as the SUA).  With proper "mains" voltages and the battery disconnected it will boot up and then fail the battery test (of course).  Appears your unit has some other problem, or in addition to, a battery problem.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

Two immediate checks:

What is the battery pack voltage? - should be ~50 volts or better

Sure you have 230 volt single phase supply of AC power - will not run on 120 volt!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:14 AM

Hi!

Thank you for your answer!

Voltage of the bettery: i'll check that.

230/120 Volts, where can i change/check that? is it possible when i remove the battery-pack, that I switch the voltage? Or when we move the USV?

br.

Lukas

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

That voltage is your "mains" voltage that the unit is plugged in to.  In the U.S., the common voltages are 240 and 120 volts.  Usually, the plug will only work with the proper voltage.  Improper wiring or grounding can cause improper voltages at the "mains" outlet.  An electrician can check this easily.  Your specific unit requires above 160 volts or so to turn on.  You can check this in your unit's specifications.

Did you check the battery pack voltage? - you need a DC voltmeter and it should read above 52 volts or so.  However, usually a "bad" battery pack (even if it's above 48 DC Volts or so) will still let the unit try to start and then fail with a bad battery warning.

Let me know what you find.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

Ok. Understand.

About the Voltage: I bought it in Europe, and the USV was in use before in Europe. So the Voltage must be 230V.

I'll check the battery. 

General question: is it possible to start the USV without battery? (To find and isolate the faults)

BR an nice week

Lukas

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

Lukas,

Unfortunately a SUA3000RMi2U will not start if the batteries are dead or disconnected. The battery cartridge is made up of 8 12v DC batteries. Each good battery should measure around 13.5v DC. If you find that some of the batteries are bad they all should be replace. You will find information on a genuine APC RBC43 at APC.com. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:39 AM . Last Modified: ‎2024-03-18 04:13 AM

I have a DLA3000RMT2U that operates at 208 volt single phase (should be same topology as the SUA).  With proper "mains" voltages and the battery disconnected it will boot up and then fail the battery test (of course).  Appears your unit has some other problem, or in addition to, a battery problem.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore