APC Smart UPS 2200 RM battery failure lead to power output interruptions

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart UPS 2200 RM battery failure lead to power output interruptions
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
wuffyma
Crewman wuffyma
Crewman

Posted: ‎2025-03-11 11:01 PM

0 Likes
7
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-11 11:01 PM

APC Smart UPS 2200 RM battery failure lead to power output interruptions

My APC Smart UPS 2200 RM power output unexpectedly interrupted due to one battery failed, resulting in the reboot of all servers connected to it.

Upon reviewing the logs, I found the following entries:

UPS: At least one faulty battery exists.
UPS: Failed a self-test.

The device was loading at below 40%, indicating that the failure of a single battery should not have caused an overload.

How to prevent this situation from occurring again? It will a nightmare if one battery failure could led to a power output interruption even after I replace with a new battery.

Model: Smart-UPS 2200 RM
Firmware Revision: 665.6.I

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Spock Teken
Spock

Posted: ‎2025-03-12 03:19 AM

0 Likes
0
439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 03:19 AM

The service life of the battery cartridge is rated for 2-5 years of service. This is based on usage, temperature, and environmental factors.

 

Simply put you'll need to replace the entire battery cartridge. If your system has extended battery packs it’s imperative that you inspect all battery cartridges and properly test each cell for AVR.

 

As it only takes a single cell to drag the rest down resulting in the condition you experienced! ☝️Which leads to affirming the need to replace battery cartridges at a defined interval and validating the system with an annual static & dynamic load test.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

wuffyma
Crewman wuffyma
Crewman

Posted: ‎2025-03-12 07:54 PM

0 Likes
1
406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 07:54 PM

Thank you Teken, you are right about the annual maintenance and entire battery replacement.

What if one of the new batteries fails suddenly? How can I prevent it from dragging the rest down and interrupting the power supply output?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-03-13 05:09 AM . Last Modified: ‎2025-03-13 05:15 AM

In response to wuffyma
0 Likes
0
372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 05:09 AM . Last Modified: ‎2025-03-13 05:15 AM

To be honest that isn’t a very common problem (IF) the cartridge is new. If we assume a few hypothetical scenarios such as receiving a bad cartridge from APC.

 

I would submit a service request to have the cartridge replaced under warranty. If the battery cartridge is not under warranty than I would take the cartridge apart.

 

Physically inspect all wiring, fuse, and cells. Than measure each one for voltage & resistance. You will find that one or more cells are not in specifications of the battery makers documentation.

 

If this was simply a short term break fix. Once identified you would replace that bad cell. Obviously, this is not best practices as mixing new and old cells will result in unexpected operational runtime and performance!

 

As an aside if best practices are in place the battery installation date would be accurate on the UPS. If by chance someone ignored the battery installation date or simply reset the counter / date.

 

All battery cartridges and cells have a production date embedded on them. ☝️Regardless of all the above a annual (Lights Out / Grid Down) validation test must be performed under load and timed.

 

This is the only true method to know how the system will operate during a power disturbance. Keep in mind both static & dynamic load testing is extremely stressful on the battery as such impacts the 260 full depletion cycles the system is rated for.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

wuffyma
Crewman wuffyma
Crewman

Posted: ‎2025-03-17 10:53 PM

0 Likes
3
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-17 10:53 PM

Is it possible to fix the auto-bypass cause output interruption by upgrading firmware? My firmware version is 665.6.I.

Or shall I get a new UPS? My UPS Manufacture Date: 10/24/09

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-03-18 03:53 AM

In response to wuffyma
0 Likes
2
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 03:53 AM

Please show me a photo of the front and back of the unit showing the model & serial number.

 

The prefix will be SAU, SMX, SMT, SRT, SURT, SMC, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

wuffyma
Crewman wuffyma
Crewman

Posted: ‎2025-03-19 08:43 PM

In response to Teken
0 Likes
1
241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 08:43 PM

Thank you so much Teken, below are the front and back photos:

Front.jpg

Back.jpg

 

By the way, will any model that use "Double-conversion on-line pure sine wave" helps solving the output interruption issue?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-03-20 03:27 AM

In response to wuffyma
0 Likes
0
228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-20 03:27 AM

Sorry I can’t see the image besides a box with a triangle error. ☹️

 

Regardless, your problem is simply a bad battery cartridge with one or more cells. The solution is to replace the entire battery pack and insure regular validation and testing.

 

A double conversion system is not going to help solve this problem.

 

The manual bypass option on some UPS Systems is used in specific cases and not intended as a substitute for a battery replacement.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of