SMT1000 firmware question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1000 firmware question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
7
4435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

SMT1000 firmware question

Hello,

I recently acquired a used SMT-1000 with a date of manufacture of 08/2011. Presently, the unit is on the UPS 06.5 (ID18) firmware. I have looked into the various processes of updating it's firmware, however I still have some questions.

According to the firmware revision matrix found in this how to article, the most up to date firmware version I could put on the unit is UPS 7.1. However, the article that describes updating the UPS firmware via the NMC shows that the correct firmware file for my unit would install UPS 9.4. In addition, when I look at the readme file for this update it does not show the list of release notes beyond UPS 09.3.

So, I guess my question is how can I tell what firmware my unit is actually compatible with? Is there a reason that the update wizard article states that it will only update my unit to UPS 0.7.1, despite the NMC method article saying that I can update to UPS 0.9.4?

Thanks in advance!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
4434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

Hi Matt - 

The only thing that matters in selecting the firmware is the ID#. Are you absolutely certain that your unit is 18 and not 17? The matrix in the article from the Firmware Upgrade Wizard is assuming that if your unit has UPS FW less than 8.0, it is an ID17 unit. 

Our recommendation for upgrading UPS FW is to use the Firmware Upgrade Wizard (via Serial) if at all possible. It includes additional system checks that are not possible when using the Network Management Card. Furthermore, on an older UPS that is out of warranty I probably wouldn't upgrade the firmware unless you are experiencing an issue of some sort. If the unit is not performing as expected, then by all means upgrade the FW, but beyond that I tend to take an "If it ain't broke, don't fix it" approach. You can use the Network Interface for the UPS while you are awaiting batteries, but I would not upgrade the firmware until you have new batteries installed in the unit.

We have release notes for many of the images, but not all. All new releases moving forwards will have release notes attached. For the FW revs that have release notes you will find them bundled with the .enc files. For UPS ID 18 image the changes are as follows:

Release Notes (UPS09.4):
========================
1.  SmartSlot card information displayed on the LCD is cleared when new card is hot-swapped 
2.  Updated LCD message in Japanese when canceling sleep.
3.  Improved robustness of serial port communications to avoid errant serial port characters from causing delayed UPS operations.
4.  LCD display operation with Legacy Communication Card (AP9620) improved to eliminate LCD display of items that are inaccessible when AP9620 is used.
5.  Improved reliability of native USB operation command DelayBeforeShutdown and switched outlet control.  
    This improves compatibility with Custom software applications, and native OS shutdown agents.
6.  Improved the cancelling of a UPS output programmed-off duration (sleep).
7.  Improved programmed-off duration (sleep) response to power outage.
Release Notes (UPS09.3):
========================
1.  Changed display of fw versions on LCD to be only the single important version number.
2.  Improved self-test logging for PCBE / NMC.
3.  Changed data reporting for future card support.
4.  Eliminated occasional false alarm when AC restored shortly after end of battery discharge.
5.  Corrected initialization of SOG status change cause variable to repair NMC logs after firmware upate.
6.  Simple Signal logic changes for Interface expander 2 support
7.  Simple Signal logic improvements to cover cases when SOG are off.
8.  Added support for OEM customer.
9.  Added factory debug capability for USB.
10. Add compatibility for IE-2 card.
11. Repaired an occasional math error in the battery replacement date algorithm that resulted in incorrect dates.
12. SOG loadshedding improved operation for canceled load shedding operations.
13. Adjustment of thresholds for AVR fault detection to increase reliability.
14. Corrected efficiency display in Japanese.
15  Increased upper end of allowed limits for Minimum Return Runtime, and Load Shed Runtime Remaining to match other Smart-UPS 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
4434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

The ID is the only thing that matters. There second document shows an ID 18 UPS 9.4 file so your UPS can be upgraded to 9.4. Perhaps the second document is newer. You can also "unzip" the firmware upgrade wizard and get all the files and pick the ID 18 one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
4434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

So I guess my next question is where I can find all of the changes between UPS 6.5 and the most current firmware.

Also, is there any harm in updating using the NIC without any batteries installed? I am presently waiting for a set to be ordered.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
4435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-18 01:27 AM

Hi Matt - 

The only thing that matters in selecting the firmware is the ID#. Are you absolutely certain that your unit is 18 and not 17? The matrix in the article from the Firmware Upgrade Wizard is assuming that if your unit has UPS FW less than 8.0, it is an ID17 unit. 

Our recommendation for upgrading UPS FW is to use the Firmware Upgrade Wizard (via Serial) if at all possible. It includes additional system checks that are not possible when using the Network Management Card. Furthermore, on an older UPS that is out of warranty I probably wouldn't upgrade the firmware unless you are experiencing an issue of some sort. If the unit is not performing as expected, then by all means upgrade the FW, but beyond that I tend to take an "If it ain't broke, don't fix it" approach. You can use the Network Interface for the UPS while you are awaiting batteries, but I would not upgrade the firmware until you have new batteries installed in the unit.

We have release notes for many of the images, but not all. All new releases moving forwards will have release notes attached. For the FW revs that have release notes you will find them bundled with the .enc files. For UPS ID 18 image the changes are as follows:

Release Notes (UPS09.4):
========================
1.  SmartSlot card information displayed on the LCD is cleared when new card is hot-swapped 
2.  Updated LCD message in Japanese when canceling sleep.
3.  Improved robustness of serial port communications to avoid errant serial port characters from causing delayed UPS operations.
4.  LCD display operation with Legacy Communication Card (AP9620) improved to eliminate LCD display of items that are inaccessible when AP9620 is used.
5.  Improved reliability of native USB operation command DelayBeforeShutdown and switched outlet control.  
    This improves compatibility with Custom software applications, and native OS shutdown agents.
6.  Improved the cancelling of a UPS output programmed-off duration (sleep).
7.  Improved programmed-off duration (sleep) response to power outage.
Release Notes (UPS09.3):
========================
1.  Changed display of fw versions on LCD to be only the single important version number.
2.  Improved self-test logging for PCBE / NMC.
3.  Changed data reporting for future card support.
4.  Eliminated occasional false alarm when AC restored shortly after end of battery discharge.
5.  Corrected initialization of SOG status change cause variable to repair NMC logs after firmware upate.
6.  Simple Signal logic changes for Interface expander 2 support
7.  Simple Signal logic improvements to cover cases when SOG are off.
8.  Added support for OEM customer.
9.  Added factory debug capability for USB.
10. Add compatibility for IE-2 card.
11. Repaired an occasional math error in the battery replacement date algorithm that resulted in incorrect dates.
12. SOG loadshedding improved operation for canceled load shedding operations.
13. Adjustment of thresholds for AVR fault detection to increase reliability.
14. Corrected efficiency display in Japanese.
15  Increased upper end of allowed limits for Minimum Return Runtime, and Load Shed Runtime Remaining to match other Smart-UPS 
Reply

Link copied. Please paste this link to share this article on your social media post.

Semipfuscher
Semipfuscher Cadet
Cadet

Posted: ‎2025-03-18 06:37 AM

0 Likes
1
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 06:37 AM

Hallo Everyone.

I have a Smart UPS SMT1000IC with UPS FW 03.5 and ID:1015.

Where i can find the right New Firmware file and can i swapped direct to the newest revision. I installed also now new Batterien on it.Did the customer load can have a load drop during this process? Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-03-18 06:49 AM

In response to Semipfuscher
0 Likes
0
1834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 06:49 AM

What is the serial number of the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Semipfuscher
Semipfuscher Cadet
Cadet

Posted: ‎2025-03-19 01:57 AM

0 Likes
1
1792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 01:57 AM

AS2106120201

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-03-19 05:02 AM

In response to Semipfuscher
0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 05:02 AM

Based on the serial number you may follow the APC Firmware FAQ:

 

https://www.apc.com/us/en/faqs/FA164737/

 

To answer the other questions you may upgrade directly from 3.5 to the latest. The output may also remain on while the UPS firmware is being loaded.

 

Having said that I can tell you from personal experience that is not a good idea! ☝️

 

If the client can power down and disconnect the loads the risks are much reduced.

 

Lastly, insure all requirements are in place and met prior to the firmware upgrade. If the hardware is under warranty this procedure should be done live over the phone with APC Technical Support.

 

If the hardware is not in warranty as seen in your serial number. You should have an exit / recovery plan in place.

 

Questions Ask . .  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.