APC Smart UPS 2200 5U rackmount strange behaviour

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart UPS 2200 5U rackmount strange behaviour
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

0 Likes
3
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

APC Smart UPS 2200 5U rackmount strange behaviour

Hi,

I'm hoping someone can help me here. I have a APC Smart UPS 2200 5U rackmount which recently has started behaving strangely. It's 5 battery status leds have started blinking together at one second intervals (on, then off all in one second) when I load it more than about 22%. Under this load, they all light together so as to indicate the batteries are fully charged. I replaced the batteries yesterday with new original APC batteries, but no change in the behaviour. The batteries I took out, also APC original, were extremely hot, in fact the whole UPS was too hot with it's fan turning on occasionally to pull the internal temperature down from about 57 degrees centigrade. With the new batteries its internal temperature has reduced to about 45 degrees, the room temperature is 22 degrees. The new batteries are not hot, however I think the cables to the first battery is a little warn, which would indicate to me that the UPS is still trying to charge the batteries 24 hours after replacing them. I started a serial console session to the UPS, at which point is switched briefly to the batteries, and the 5 battery leds stopped flashing, and only the bottom of the 5 leds was now flashing. Via the serial console, I told the UPS to do a recalibrate using the "D" character, however it responded with NO, and refused to do it. I pulled the plug and the UPS immediately indicated by repeatedly beeping twice per second that the battery charge was too low and an imminent shutdown was to happen. The load here was at 22%. I monitored the charge on my systems and was able to see that after almost two hours, the battery voltage was starting to drop enough that it would be a problem, so I plugged it in again. The battery charge 24 hours after replacing the batteries is 100%, however the UPS thinks there is only 2 minutes left on the batteries. I would like to do a recalibrate here as to me that would seem the next logical step in addressing this problem, however it seems not possible. I am using apcupsd on an old Linux installation.

Does anyone know anything that might help me here? Do I only need to get it to recalibrate, or has my UPS developed some kind of obscure defect? I will be grateful for any information.


DATE : Thu Jul 21 19:27:52 CEST 2011
HOSTNAME : midori
RELEASE : 3.10.6
VERSION : 3.10.6 (10 October 2003) suse
UPSNAME : SMART_UPS_2200INET
CABLE : Custom Cable Smart
MODEL : SMART-UPS 2200 RM
UPSMODE : Stand Alone
STARTTIME: Thu Mar 17 23:16:00 CET 2011
STATUS : ONLINE LOWBATT
LINEV : 223.6 Volts
LOADPCT : 23.4 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 2.0 Minutes
MBATTCHG : 0 Percent
MINTIMEL : 0 Minutes
MAXTIME : 3600 Seconds
MAXLINEV : 226.2 Volts
MINLINEV : 223.6 Volts
OUTPUTV : 223.6 Volts
SENSE : Medium
DWAKE : 000 Seconds
DSHUTD : 300 Seconds
DLOWBATT : 02 Minutes
LOTRANS : 196.0 Volts
HITRANS : 253.0 Volts
RETPCT : 015.0 Percent
ITEMP : 45.9 C Internal
ALARMDEL : 5 seconds
BATTV : 54.5 Volts
LINEFREQ : 50.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 12
XONBATT : Wed Jun 29 12:45:11 CEST 2011
TONBATT : 0 seconds
CUMONBATT: 65 seconds
XOFFBATT : Wed Jun 29 12:45:14 CEST 2011
LASTSTEST: Wed Jun 29 12:45:11 CEST 2011
SELFTEST : NO
STESTI : 336
STATFLAG : 0x02010048 Status Flag
DIPSW : 0x00 Dip Switch
REG1 : 0x00 Register 1
REG2 : 0x00 Register 2
REG3 : 0x00 Register 3
MANDATE : 07/18/96
SERIALNO : GS9630054844
BATTDATE : 07/18/96
NOMOUTV : 230
NOMBATTV : 48.0
EXTBATTS : 0
FIRMWARE : 82.8.I
APCMODEL : MWI
END APC : Thu Jul 21 19:28:30 CEST 2011

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

yes, thats fine. i would like you to try a different procedure but using the same port settings. i will private message you those instructions which you can get to on the top right of the screen near your profile settings. some people sometimes cant find the envelope icon ๐Ÿ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

can you get us the exact model number off the white sticker on the unit? i am guessing something like SU5000RMT5U or similar.

what were you trying to do with the "D" character exactly?

the flashing battery bar graph indicates insufficient runtime. its trying to tell you that your availabile runtime is within 2 minutes of your low battery setting (which by default is 2 minutes). based on your apcupsd readout, yours is still set to two minutes. this generally happens with older batteries and sometimes we do need to reset the UPS to make sure it knows you replaced the batteries, if it does not happen automatically.

let me know that exact model of UPS and what you were trying to do with that D character so i know what happened so far and we can go from there. should not be an issue to fix this as i do not think it is more than a cosmetic issue/setting that we just need to adjust (based on what i understand so far).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

Thanks for your reply. It's a Smart-UPS 2200RMINET.

I got the "D" command from following the apcupsd user manual, recalibration section, http://www.apcupsd.com/manual/manual.html#recalibrating-the-ups-runtime

Is this enough information for you?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

0 Likes
0
611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 02:20 AM . Last Modified: โ€Ž2024-03-10 11:48 PM

yes, thats fine. i would like you to try a different procedure but using the same port settings. i will private message you those instructions which you can get to on the top right of the screen near your profile settings. some people sometimes cant find the envelope icon ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of