Hi
I just wanted to ask, is it normal for the Smart 1500 SC to buzz when on battery? It's quiet otherwise. More importantly, I noticed the server power-supply also emits a similar buzzing when the ups is on battery (this too is quiet when on mains power). I was concerned I might be dramatically reducing the life of the server power-supply somehow?
The buzzing itself is fairly loud, not very, but enough to make me wonder if i've just purchased a faulty unit.
There's only the one server on the Smart 1500, it's an HP ProLiant ML110 G4.
Thank you
Steve
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
"For the duration your PSU operates on it, it shouldn't affect service life."
Where I live there can be power-cuts every day. Sometimes they last for 5 minutes, other times they can last for hours.
With just the one server on the Smart 1500, it can stay running on battery for 60+ minutes...the PowerChute software has 2 options for auto-shutdown - on "battery limit" or "60 minutes" (max allowable value in the box). I currently have it set to shutdown after 45 minutes on battery.
You use the words "shouldn't affect"...would I be better off having the server auto-shutdown after...15 minutes? Is the buzzing going to shorten the life of the server PSU if it did it every day ?
Thanks
Steve.
Message was edited by: SteveB
Message was edited by: SteveB
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Hello,
What is the power capacity (in Watts) of the server? Is the software reporting that you have 60 minutes of runtime available? That figure seems a little high, as you would normally see 45 minutes tops with approximately a 400W server, if not less. Again, the buzzing is most likely in response to the step-approximated sine wave, and may or may not be damaging to the PSU on the server. You should contact your server manufacturer for more details on how that can affect the overall performance and life expectancy of the server.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:04 AM
Hi
Looking at the PSU in the server, it's rated at 300W for 12V and 130W for 3.3V (it's what came with the ML110 G4 when it was bought).
The PowerChute software reports load to be at 7% with 119 minutes of Runtime Remaining. This figure usually drops quite quickly (at least initially before stabilising at a slower decay) when the mains power does actually fail, but I am confident it'll do at least 60 minutes before the battery is exhausted.
If having the server on battery for prolonged periods (> 10 minutes at a time) is infact "damaging", then it seems i've invested in a $500 UPS that actually shortens the life of my server π
Steve
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
@KVAr - ok, that's useful to know, i've adjusted the PowerChute "automatically shutdown server after X minutes on battery" to 30. This should keep the server PSU happy and the battery in reasonable condition for as long as possible.
Thanks to both of you for your time, much appreciated π
Steve.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
@KVAr - ok, that's useful to know, i've adjusted the PowerChute "automatically shutdown server after X minutes on battery" to 30. This should keep the server PSU happy and the battery in reasonable condition for as long as possible.
Thanks to both of you for your time, much appreciated π
Steve.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 06:27 AM . Last Modified: β2024-03-08 12:03 AM
Hi
I just wanted to ask, is it normal for the Smart 1500 SC to buzz when on battery? It's quiet otherwise. More importantly, I noticed the server power-supply also emits a similar buzzing when the ups is on battery (this too is quiet when on mains power). I was concerned I might be dramatically reducing the life of the server power-supply somehow?
The buzzing itself is fairly loud, not very, but enough to make me wonder if i've just purchased a faulty unit.
There's only the one server on the Smart 1500, it's an HP ProLiant ML110 G4.
Thank you
Steve