APC Smart 1500 SC - buzzing whilst on battery - normal?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart 1500 SC - buzzing whilst on battery - normal?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

0 Likes
9
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

APC Smart 1500 SC - buzzing whilst on battery - normal?

Hi

I just wanted to ask, is it normal for the Smart 1500 SC to buzz when on battery? It's quiet otherwise. More importantly, I noticed the server power-supply also emits a similar buzzing when the ups is on battery (this too is quiet when on mains power). I was concerned I might be dramatically reducing the life of the server power-supply somehow?

The buzzing itself is fairly loud, not very, but enough to make me wonder if i've just purchased a faulty unit.

There's only the one server on the Smart 1500, it's an HP ProLiant ML110 G4.

Thank you

Steve

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1500
  • buzz
  • buzzing
  • smart
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

SteveB wrote:
"For the duration your PSU operates on it, it shouldn't affect service life."

Where I live there can be power-cuts every day. Sometimes they last for 5 minutes, other times they can last for hours.

With just the one server on the Smart 1500, it can stay running on battery for 60+ minutes...the PowerChute software has 2 options for auto-shutdown - on "battery limit" or "60 minutes" (max allowable value in the box). I currently have it set to shutdown after 45 minutes on battery.

You use the words "shouldn't affect"...would I be better off having the server auto-shutdown after...15 minutes? Is the buzzing going to shorten the life of the server PSU if it did it every day ?

Thanks

Steve.
I meant that it's not running on modified squarewave 24/7/365. Couple hours a week should not pose a problem. Since you have frequent outages, I would at least quadruple the runtime reserve. So, if you frequently have 30 minutes outages, get something that gives you 2 hours of runtime. Your battery will not last long at all if it's allowed to discharge deeply frequently.

Message was edited by: KVAr

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

SteveB wrote:
Hi

I just wanted to ask, is it normal for the Smart 1500 SC to buzz when on battery? It's quiet otherwise. More importantly, I noticed the server power-supply also emits a similar buzzing when the ups is on battery (this too is quiet when on mains power). I was concerned I might be dramatically reducing the life of the server power-supply somehow?

The buzzing itself is fairly loud, not very, but enough to make me wonder if i've just purchased a faulty unit.

There's only the one server on the Smart 1500, it's an HP ProLiant ML110 G4.

Thank you

Steve
Buzzing from the UPS itself is normal. Modified square-wave type UPS will make buzzing sound and cause the PSU to emit a similar sound.

Sinewave UPS tend to hum rather than buzz and it does not make the PSU make any unusual noise.

The SC line of Smart-UPS is the economy version that puts out a modified squarewave, like the red graph. Modified sinewave would look more like sinewave simulated in multiple steps in ascending and descending, but marketing literature would usually call modified squarewave as "modified sinewave"

The noise is caused by sudden rise and fall in voltage in waveform. For the duration your PSU operates on it, it shouldn't affect service life.

http://img142.imageshack.us/img142/2597/waveforms600hi3.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

"For the duration your PSU operates on it, it shouldn't affect service life."

Where I live there can be power-cuts every day. Sometimes they last for 5 minutes, other times they can last for hours.

With just the one server on the Smart 1500, it can stay running on battery for 60+ minutes...the PowerChute software has 2 options for auto-shutdown - on "battery limit" or "60 minutes" (max allowable value in the box). I currently have it set to shutdown after 45 minutes on battery.

You use the words "shouldn't affect"...would I be better off having the server auto-shutdown after...15 minutes? Is the buzzing going to shorten the life of the server PSU if it did it every day ?

Thanks

Steve.

Message was edited by: SteveB

Message was edited by: SteveB

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

Hello,

What is the power capacity (in Watts) of the server? Is the software reporting that you have 60 minutes of runtime available? That figure seems a little high, as you would normally see 45 minutes tops with approximately a 400W server, if not less. Again, the buzzing is most likely in response to the step-approximated sine wave, and may or may not be damaging to the PSU on the server. You should contact your server manufacturer for more details on how that can affect the overall performance and life expectancy of the server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:04 AM

Hi

Looking at the PSU in the server, it's rated at 300W for 12V and 130W for 3.3V (it's what came with the ML110 G4 when it was bought).

The PowerChute software reports load to be at 7% with 119 minutes of Runtime Remaining. This figure usually drops quite quickly (at least initially before stabilising at a slower decay) when the mains power does actually fail, but I am confident it'll do at least 60 minutes before the battery is exhausted.

If having the server on battery for prolonged periods (> 10 minutes at a time) is infact "damaging", then it seems i've invested in a $500 UPS that actually shortens the life of my server 😞

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

SteveB wrote:
"For the duration your PSU operates on it, it shouldn't affect service life."

Where I live there can be power-cuts every day. Sometimes they last for 5 minutes, other times they can last for hours.

With just the one server on the Smart 1500, it can stay running on battery for 60+ minutes...the PowerChute software has 2 options for auto-shutdown - on "battery limit" or "60 minutes" (max allowable value in the box). I currently have it set to shutdown after 45 minutes on battery.

You use the words "shouldn't affect"...would I be better off having the server auto-shutdown after...15 minutes? Is the buzzing going to shorten the life of the server PSU if it did it every day ?

Thanks

Steve.
I meant that it's not running on modified squarewave 24/7/365. Couple hours a week should not pose a problem. Since you have frequent outages, I would at least quadruple the runtime reserve. So, if you frequently have 30 minutes outages, get something that gives you 2 hours of runtime. Your battery will not last long at all if it's allowed to discharge deeply frequently.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

@KVAr - ok, that's useful to know, i've adjusted the PowerChute "automatically shutdown server after X minutes on battery" to 30. This should keep the server PSU happy and the battery in reasonable condition for as long as possible.

Thanks to both of you for your time, much appreciated πŸ™‚

Steve.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

@KVAr - ok, that's useful to know, i've adjusted the PowerChute "automatically shutdown server after X minutes on battery" to 30. This should keep the server PSU happy and the battery in reasonable condition for as long as possible.

Thanks to both of you for your time, much appreciated πŸ™‚

Steve.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

SteveB wrote:
@KVAr - ok, that's useful to know, i've adjusted the PowerChute "automatically shutdown server after X minutes on battery" to 30. This should keep the server PSU happy and the battery in reasonable condition for as long as possible.

Thanks to both of you for your time, much appreciated πŸ™‚

Steve.
To clarify, I gave 30 minutes as being 25% of 2 hours. If you have very frequent long outages, set it for about 25% of maximum runtime. If you can only get an hour, then set it for 15 minutes. If this doesn't work out, you may want to get something like a SU1000XL refurb or a brand new SUA1000XL.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:27 AM . Last Modified: β€Ž2024-03-08 12:03 AM

Hi

I just wanted to ask, is it normal for the Smart 1500 SC to buzz when on battery? It's quiet otherwise. More importantly, I noticed the server power-supply also emits a similar buzzing when the ups is on battery (this too is quiet when on mains power). I was concerned I might be dramatically reducing the life of the server power-supply somehow?

The buzzing itself is fairly loud, not very, but enough to make me wonder if i've just purchased a faulty unit.

There's only the one server on the Smart 1500, it's an HP ProLiant ML110 G4.

Thank you

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of