APC SUA 2200 won't power on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SUA 2200 won't power on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

0 Likes
8
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

APC SUA 2200 won't power on

Hello,

I came on-site to a job yesterday and one of the APC 2200's was no longer powered on. I installed/configured the UPS a little over a week ago successfully with no issues. When I came in yesterday the UPS was powered off completely.

I thought it was the outlet(s) in the room but the two Cisco switches for which it's supposed to be supplying power were now using the outlets instead of plugging into the UPS (I guess someone else did this).

The only response I'm getting from the UPS is that it'll chirp very intermittently (like every 10 sec) and when it chirps all the lights on the front control panel flash. That's the only activitly I get from it. I've tried holding in both the Test (power on) button and holding in the power off button but no success. I've disconnect/re-connected the battery, but still unable to obtain utility power. I'm not really sure what's going on. Any ideas?

It is very hot in the room that it is in since there is no AC in the building yet so I wasn't sure if that had any relevence to the problem. Any insight would be helpful! Thanks!

Message was edited by: myentsch

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • battery
  • beeping
  • hardware
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

I'm not getting any power to the unit. Would this still be possible? If so, could it be access using the web interface or would I have to console into it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

0 Likes
0
1745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

I'm not getting any power to the unit. Would this still be possible? If so, could it be access using the web interface or would I have to console into it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:17 PM

Hi myentsch, could we get the full model and serial number of the UPS to get an idea exactly what we are dealing with. Regardless of where the ups is plugged (or even if it is plugged in) the UPS should be able to cold start. Since it appears the UPS is not able to do that we would first want to look at the batteries in the UPS. (IE try to get the battery voltage and/or if possible try to swap the bats out with some form a know working unit). Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

Hi Mike,

Let us start with getting the Model and Serial number of the UPS. This would help us to properly troubleshoot the correct UPS.

When you deployed the UPS, did it come with a network management card or have you installed PowerChute Business Edition? These two would help us retrieve important log files that would tell us what the UPS has encountered. I would also advise to check the battery, I would like to know if the battery is bloated or if it is leaking.

You have mentioned that the UPS chirps, when does it chirps? Is it when it is connected to the power source or does it do it when you press a button? When it comes to the LED indicators, does all LED flash or there's just a couple?

As much as possible, the UPS should be deployed on a good operating environment. Failure to do so might cause an issue or damage with the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

If you do have a spare battery you can try it and if it is the same thing, the UPS needs replacement already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

I'm not on-site at the momem so I don't have the serial #, but the model is an APC SUA 2200R3XLNETPKG.

To answer your questions:

- Yes, it has a network management card installed and no, I have not installed the PowerChute Business Edition. The battery's physical condition looked OK when I checked yesterday. I wasn't able to swap in a battery from a working unit while on-site though.

- The chirping is a consistent chirp with about 10 sec intervals.

- Pressing either button while connected to its utility power does nothing. No sounds, no lights on the control panel flash, or anything.

- All LED indicators light up when it chirps. That's the only time they light up.

Hope this gives you a better idea. Thanks for the response!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

If you can access the network management card, it would help if you can download the event.txt, data.txt and config.ini files. You can then post it here and you can remove the IP settings if you want.

These files would help us see if the UPS has logged anything about the issue that you've experienced.

To assist you on how to download it, here is the link [How can I download Event logs and Data logs and Config.ini from the Network Management Card?|http://nam-en.apc.com/app/answers/detail/a_id/9321/kw/nmc%20event%20logs/session/L3RpbWUvMTMwNjMzNTY...]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

If the LED's on the NMC still lits up, we can try to access it using web,ftp and console.

Let us try to do the following:

- Remove all the load on the UPS and turn if off. Unplug the UPS from the utility outlet.
- Press and hold the O/Off button for around 5 seconds or until you hear a click
- Press and hold the I/Test button, you would normally hear a short and a long beep. As soon as you hear the long beep release the button.

The last step should force the UPS to run on battery, let us know what will happen. If the issue persist, I suggest that you call our Tech Support to verify the warranty and if possible a replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:35 AM . Last Modified: ‎2024-03-10 11:16 PM

@JonPro

I tried the steps you suggested, but no success. No difference. Still chirps even when it's not plugged into the wall.

The only other thing I can think of now is to swap in a battery from a working UPS.

Any thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.