APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
We're using XLT model to support our computer systems. UPS units bought in USA but used in Europe. The model spec says 208-240 adjustable input voltage but APC in Europe told us that we cannot use this unit in Europe since it is designed for US. They told us that they meant phase-to-phase 208 VAC. Units were failed when we hook up units to 220 V single phase, they all failed. Didn't make too much sense to me, is it really true? Does anybody have any idea about this issue?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
after investigation, an SURT UPS does not care if it is fed 2 phases and a ground or phase, ground, and neutral. the only major differences are things like breakers and plug types and on board firmware.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:21 AM . Last Modified: 2024-03-13 05:42 AM
after investigation, an SURT UPS does not care if it is fed 2 phases and a ground or phase, ground, and neutral. the only major differences are things like breakers and plug types and on board firmware.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.