APC SRT5KRMXLI - Error P.13 after battery change

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SRT5KRMXLI - Error P.13 after battery change
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Field-Ops-Cooper
Field-Ops-Cooper
Cadet

Posted: ‎2024-02-13 09:01 AM

0 Likes
3
18921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-13 09:01 AM

APC SRT5KRMXLI - Error P.13 after battery change

With no mains input voltage applied and no load connected, the batteries were swapped and then the mains input voltage restored (via the breaker). The UPS starts but immediately gives Error P.13 code with warning sound. In the menu's, under UPS Control, it gives 'UPS is in fault state', 'Output Off'

Batteries are reading good quality and 91% charged, input voltage all ok but can't clear the error state,

Any ideas how to clear it. ?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-02-14 06:27 AM

0 Likes
2
18913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-14 06:27 AM

From personal experience and what others have stated on the Internet you should contact APC Support for possible next steps if the unit is still under warranty.

 

If the hardware is NOT under warranty you may try the steps outlined below:

 

Power down and disconnect all loads from the system. Remove AC Mains from the wall outlet, internal battery, including any extended battery packs.

 

Press and hold the power button and wait for a click / beep. Doing so will complete what APC calls a Brain Dead reset.

 

Apply AC Mains only by connecting the wall plug. Press the power button and report back if the the P.13 fault has cleared.

 

If not read the user manual as to how to configure and use the EPO feature. Essentially you’re going to connect the EPO plug to the UPS. While the unit is running you will engage the EPO which will immediately shut down the UPS.

 

Wait about ten seconds and then press the power button. The UPS will beep, LCD should indicate EPO something and to press any button to clear the fault.

 


Is the P.13 fault present?

 

If yes the last step is to attempt to default the UPS to a factory state. You can try doing this through the LCD menu. If that doesn’t work you can try the same over serial (CLI) and select the option to default the unit.

 

NOTE: If there is a NMC (Network Management Card) installed download both error logs. Using the NMC report back what happens when you turn on the grouped outputs?

 

Self Test: If the unit is programmed to complete a self test disable the same. Either through the LCD Menu, CLI, or NMC. Doing so will help you complete the three different procedures without the system running this conflicting process.

 

Report back the results!

Reply

Link copied. Please paste this link to share this article on your social media post.

Field-Ops-Cooper
Field-Ops-Cooper
Cadet

Posted: ‎2024-02-20 12:31 PM

In response to Teken
0 Likes
1
18880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-20 12:31 PM

Powered down and disconnect all loads from the system. Removed AC Mains connection, & internal batteries (no extended batteries connected)

Pressed and held power button, but no click or bleep.
Reconnected Mains AC and still getting Error P.13.

Will try consoling in as next stage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Manuel_Martin
Manuel_Martin
Cadet

Posted: ‎2025-01-07 04:47 AM

In response to Field-Ops-Cooper
0 Likes
0
10493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-07 04:47 AM

Ontem encontrei um equipamento com essa mesma falha. Pelo que consegui pesquisando, indica problema no circuito inversor. Ou seja, terá que retirar a placa em bancada e efetuar o conserto. Somente por programação e limpeza de alarmes não resolve.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.